Questions tagged [delta]

73 questions
15
votes
4 answers

Why does a delta/wye transformer make 30 degrees phase shift ?

I'v heard that a delta/delta or Wye/Wye transformers do not make any phase shift. In delta/wye or wye/delta transformers, There is a 30 degrees phase shift between the primary and secondary coils. So, Why is there a phase shift ? and Why is it 30…
Michael George
  • 3,742
  • 13
  • 53
  • 84
10
votes
4 answers

Can I drive a 3-wire-delta-input appliance with a wye-output transformer?

We have a high-current industrial machine rated for 3-phase at 230 V; the nameplate literally says "PHASES: 3Ph + PE", "VOLTAGE: 3X230VAC", and "FULL LOAD: 92A". There are only three input terminals (neglecting the PE, which is attached to the…
bernz
  • 203
  • 6
7
votes
2 answers

I need help understanding the total impedance in a delta connection

I'm trying to upskill by teaching myself electrical engineering. I already have a degree in theoretical physics and pure mathematics so I don't mind math-heavy answers. While I don't find the maths of the electronics problems I've encountered so…
Jamie OM
  • 71
  • 1
6
votes
2 answers

Three-phase motor Delta/YY connection diagram and windings troubleshooting

I am trying to troubleshoot this 1.4 kW three-phase motor and I'm unsure how its internal windings are interconnected or whether they are shorted. On the plate it says "Delta/YY 400 V", and I'm not sure what YY means. Most articles online describe…
Robert Lee
  • 205
  • 1
  • 5
4
votes
0 answers

Zero current assumption in star - delta transformations derivations

The formula used for star delta transformations are: $$ R_A = \frac{R_{AB} R_{AC}}{R_{AB}+R_{AC}+R_{BC}} $$ and $$ R_{AB} = \frac{R_AR_B + R_AR_C + R_BR_C}{R_C} $$ The normal way that these formulae are derived is by equating the expressions for…
Balu
  • 43
  • 5
4
votes
1 answer

Why choose delta over star connection for a 3 phase motor with a VFD?

With respect to a particular application, why is it better to use a delta connection over a star? I have a motor/pump hooked up to a vfd in delta. For my application, Im required to adjust the flow rate of the water in the pipeline. The motor was in…
Luqmaan
  • 55
  • 1
  • 2
  • 8
4
votes
1 answer

What are the Pros/Cons on the 30 Degree voltage phase shift between the primary and secondary of a Delta-Wye Transformer

I have searched this wonderfully informative website and learned much about Delta-Wye connections and why a phase shift in voltage would exist between the two. I am also aware that both Delta-Delta and Wye-Wye connections do not have this phase…
BLUEJAYS13
  • 41
  • 3
3
votes
1 answer

3 Phase "Black Box" Load

I'm doing a few basic load calculations on a 3 phase circuit at work and I stumbled on a concept I'm not sure how to proceed. Let's say you have a 3 phase load and it is basically a black box. For many reasons, you don't have any access to the…
3
votes
1 answer

Confusion with applying KCL to three phase delta connection

Below is a 3-phase delta connected for balanced loads Z: Since phase-to-phase voltages (voltage across loads) have 120 degrees phase differences and since the loads have the same impedance we can conclude that the currents Iux, Izw, Ivy across the…
user1245
  • 3,955
  • 4
  • 37
  • 87
3
votes
2 answers

Dab vs Dac transformer

simulate this circuit – Schematic created using CircuitLab Why might one use a delta-wye transformer with the delta configured in Dab rather than Dac, or vise versa? Will this cause a difference in phase sequence? In Dab, coil A's non-polarity side…
nmorris
  • 85
  • 2
  • 7
2
votes
1 answer

Derivative of a waveform

I am self studying linear circuits and I came to a very basic problem. The problem: $$y(t) = e^{-t} u(t)$$ where \$u(t)\$ is the step function. Calculate the derivative of \$y(t)^{\prime}\$. My take is: $$ \begin{align} y(t)^{\prime} & =\left(…
2
votes
1 answer

Why is one current reading ~20% higher than the other two in a balanced high-leg delta load?

We are using eGuage watthourmeters to monitor the outdoor unit on five VRF systems powered by two different 3P4W 120/208V high-leg delta panels. The neutral is not connected to the outdoor units. We have connected the meters according to the…
LShaver
  • 841
  • 1
  • 13
  • 28
2
votes
2 answers

Delta-Star Combination Exercise

This post is regarding exersise 4-8 from the following book: Hughes Electrical And Electronics Technology 10th Ed. Here it is: Let's focus on what I tried for solving part (b) : Since this is an exercise under the chapter for delta-star…
Stamatis
  • 135
  • 3
2
votes
2 answers

Motors Delta/Star connections to VFD

I've selected 230/400V motors (delta/star) and corresponding 400V VFDs for pump motors. Now I've been asked why I haven't selected 400/690V motors (delta/star), that are the standard and usually connected in delta. The manufacturer says there that…
2
votes
1 answer

Why don't the currents clash in a 3 phase delta connection?

Consider 3 windings, a, b and c. L1 is connected to A, L2 to B and L3 to C. The 3 windings are then connected in delta. If we could freeze frame the voltage waveform where L1 and L2 are positive maximum and L3 is negative, what will the current…
Ph3ng
  • 337
  • 1
  • 9
  • 20