In power systems, there are rules and regulations stating what levels of harmonic distortion is acceptable. One example I've seen for voltage distortion is: THD < 8%, single component harmonic <5%. These values are (hopefully) not random numbers.
From Schneider Electric:
Harmonics are unwanted currents that overload wiring and transformers, creating heat and, in extreme cases, fire. These currents are harmful to equipment. They weaken the reliability and shorten the life expectancy of equipment exposed to the distortion
For induction machines, negative sequence harmonic currents will also cause a negative torque, which of course isn't good.
My question is: How bad is it, really? What can the consequences be if the total harmonic voltage distortion is 10% instead of 8%, if the 7th harmonic is 6% or if the negative 5th harmonic current is 10%. The reason why I ask is: Reducing harmonics does not come for free, is it really worth it in all cases? I know I have to adhere to the regulations, but assuming there were no regulations, what then?
Does anyone have any experience in this area?
Update
I forgot to mention the following in the question: The system I'm studying is not connected to the main grid. It has its own generators, UPS-system and all other necessary infrastructure. The operator and the owner of the system is the same company. The specific regulations I'm mentioning are for such isolated systems, not systems connected to the main grid (could for instance be a vessel).
Update 2
If you have your own power grid, and all the equipment is your own (thus you would need to take all the costs of installation, maintenance etc), then why are there limits and not guidelines when it comes to harmonics? I understand why there are rules regarding for instance short-circuit levels, arc-flash hazard etc. etc. I also understand regulations regarding voltage drops, as this may lead to motors stalling, loss of excitation and more, I just don't get why there are strict regulations when it comes to harmonics.
How much damage can it do?
Stewie Griffin
  • 1,547
  • Since this is a power systems question, may I suggest application of the power-distribution tag? – Li-aung Yip Jan 23 '14 at 09:48
  • @Li-aungYip: See the updated question. I should probably have added a few more details before posting the question. – Stewie Griffin Jan 23 '14 at 12:45
  • I'd say the same considerations still apply - you are still trying to keep your harmonics within the "compatibility level" that your equipment can tolerate. The only difference is that you don't have to share the network (and the harmonics emission allocation) with other customers. – Li-aung Yip Jan 24 '14 at 10:05
  • @Li-aungYip: I agree. The intention of my question was to try to understand what consequences violation of the "compatibility levels" would have. Except for relay tripping, I seriously doubt that any equipment will stop working due to harmonics when looking at a short perspective, not days, weeks, years or decades). I would think it only have long-term effects (years or decades, again except for relay tripping), but how serious are those effects? How much will it reduce the lifetime of the equipment? – Stewie Griffin Jan 24 '14 at 10:46
  • @Li-aungYip: Btw, thanks for your comments and answer, I really appreciate it! I've updated the question one more time =) – Stewie Griffin Jan 24 '14 at 10:53
  • I think that really, the rules are there to keep you from shooting yourself in the foot. All kinds of bad things happen to you when you have excessive harmonic distortion (see edits below.) I can't quantify *exactly how bad* these things are, or *exactly how fast* the damage would accumulate, but you certainly wouldn't want to run a plant with high harmonics on a long-term basis. – Li-aung Yip Jan 24 '14 at 14:27
Note: I am not an expert in harmonics.
It's valid to ask why the harmonics levels are set to the exact level they are.
I am currently reading AS 61000.3.6 (internationally, IEC 61000.3.6) which is about the nitty-gritty details of how the utilities calculate the harmonics emission limits for MV/HV/EHV customers.
Basically, it goes like this:
  • Compatibility levels: Equipment is designed to tolerate / be immune to harmonic distortion up to some level, the compatibility level. If we can keep the power system harmonic levels below the compatibility levels, the equipment will work. (The compatibility levels are defined in IEC 61000.2.2 and IEC 61000.2.12.)
    The harmonic effects being controlled are long-term effects (overheating of cables, motors, transfomers, capacitors, etc.) over a period of minutes, and short-term effects on electronic devices over a period of seconds.
  • Planning levels: If we keep the amount of harmonic emissions at 'Timbuktu substation' to '10 units' or less, we will meet the compatibility levels. (IEC 61000.3.6 goes into detail about how to calculate '10 units'.)
  • Apportionment of planning level to individual customers: Bob's Factory is using '5 units' of power, out of '10 units' available at 'Timbuktu substation'. We will allow Bob's Factory to emit a maximum of '5 units' of harmonics.
The key point is that the objective of the harmonics emission limits is to ensure that the compatibility limits aren't violated.
If each customer respects the harmonics emission limit assigned to them, then the harmonics emission level of the system as a whole will be less than the compatibility level, and everyone's equipment will work. If you exceed your emissions limit, you'll probably bugger it up for everyone.
EDIT:
You ask why there are limits on harmonics, even within your own islanded installation, where you won't be affecting other customers.
From Schneider's Cahier Technique 199 Power Quality we have the following list of negative effects from harmonics:
From Schneider's Cahier Technique No. 152, Harmonic disturbances in networks, and their treatment, we have a few more effects not mentioned above:
2.1 Instantaneous effects
Harmonic voltages can disturb controllers used in electronic systems. They can, for example, affect thyristor switching conditions by displacing the zero-crossing of the voltage wave (see IEC 146-2 and Schneider Electric "Cahier Technique" n°141).
Interference on communication and control circuits (telephone, control and monitoring)
Disturbances are observed when communication or control circuits are run along side power distribution circuits carrying distorted currents...
Some of these effects might be severe. For example, if harmonics were so bad as to cause interference on a critical control circuit, causing maloperation of that circuit, that would be bad regardless of its effect (or not) on other customers.
So, from this perspective, the limits are there to force you to consider electromagnetic compatibility with vulnerable equipment in your own installation.
Anecdotally, dirty power supplies cause all kinds of intermittent and hard-to-find issues.
My boss told me a story about how they installed a plant full of VSD's (VVVF drives) with no harmonic filtering. The problem was that substations would trip on earth fault (?) seemingly at random when drives were started up - including substations on the far side of the plant to the VSD being started!
Eventually it was determined that the relays were mal-operating due to harmonic currents. From memory, the harmonic current were flowing through the entire plant via earth paths, including structural metalwork and metal cable trays, which is why a VSD on one side of the plant was able to affect a substation on the other side. The electrical paths had to be broken up by replacing some sections of metal tray with plastic trays, and so on.
In the end the problem was only solved after an expensive course of rectification works was performed. Again, the limits are there to ensure that you have to consider harmonics from the start, so this doesn't happen to you!
Li-aung Yip
  • 8,931
  • 50
  • @RobertP. : It's a pleasure. Keep the questions coming! (And feel free to talk in the EE.SE chat room, where I can be found most of the time.) – Li-aung Yip Jan 24 '14 at 14:42
The power companies want you to reduce harmonics in your loads/appliances because those harmonics are not billable. If you mathematically multiplied your clean voltage waveform by the current waveform (which contained harmonics), only the primary frequency of the current would result in a power that had an average (and is billable). The other currents do not contribute to power output of your machine/load/appliance BUT the copper wires to your premises have to be thick enough to take this extra current.
It's all part of power factor correction and one of its primary aims is to reduce losses and save money.
If these harmonics were whizzing up and down the wiring in your house/building there might also be an EMC radiation issue and certain equipment might be interfered with too.
As for voltage waveform distortion - you, as a customer would not want this because it may lead to excess heat being generated by motors (due to the higher harmonics) so I'd say the voltage harmonic distortion limits are there to protect the consumer as much as anything else.
  • Thanks for you answer Andy! I forgot to mention one thing in the question; this is not a system connected to the transmission system, thus the interest of power systems is not really relevant in this case. I agree with you on the part about reducing losses, but the cost compared to installing equipment aimed at reducing harmonics may be higher. Therefore, I believe there are other aspects to this that may be more important in this case. I made an update to the question to make it more clear. – Stewie Griffin Jan 23 '14 at 12:43
  • The statement that harmonics are not billable is not entirely true. Harmonics degrade the power factor, and in many areas, large commercial customers have to pay surcharges for poor power factor or reactive power. In any case, harmonics incur costs to the power company which have to be paid for by its customers. So reduction of harmonics is to some degree in everyone's interest. – user28910 Jan 24 '14 at 15:17
  • @user28910. Households won't get billed in uk (yet lol) and what I'm trying to say is that there is not a direct bill for harmonics but as you say some folk get billed on poor PF. – Andy aka Jan 24 '14 at 15:26
Short answer, increased harmonics in the load ( High capacitance, or inductance) cause the voltage and current curves to get out of phase by as much as 90 degrees. When this happens the voltage is zero when the current is at its peek, and vice-versa. The result is an increase in Resistance ${R_total= \sqrt{R^2+(C_r-L_r)^2}}$ Increased resistance means increased heat generation which can cause winding failure. So yes high harmonics are bad. Utilities have large banks of capacitors and inductors which allow them to regulate harmonics. You don't. So if you own your generator they are really bad. Make sure that you balance your capacitive and inductive loads.
Chris
  • 151