3

I am looking at sub electricity meters. Right now I am reading about the ABB product line EQ. In the documentation (link to PDF, "Electricity Meters - For modular enclosures and DIN rail"), they split the products into two categories, the ones that are "transformer connected" and the ones that are "direct connected".

If I read the documentation correctly, they also call the "transformer connected" by the acronym "CTVT". I've tried to look this up, also without luck.

What does that mean?

I only know a bit more than highschool physics, so please try to give an answer that a non-engineer can understand. If that is possible :)

Mads Skjern
  • 710
  • 4
  • 14
  • 31
  • 1
    I've seen the acronym "CTVT" to stand for "Column Type Variable Transformer", but I'm thinking Spehro is probably correct in this context with "Current Transformer" and "Voltage Transformer" connected for power measurement. – Tut Jan 20 '14 at 15:13

2 Answers2

6

In order to measure power (and sum that up to get the energy flow), the instrument needs to measure both the voltage and the current.

When voltages and currents are relatively low, it makes sense to run wires directly to the instrument, hence "direct connected". If the currents are relatively large, the wires become thick and expensive, and the control panel might be a bit remote. Also, the connections on a typical instrument won't handle very high currents. Such high currents can also be quite dangerous because fault currents could be high enough to cause arc flash injuries. So, a Current Transformer (CT) is installed on the high current line (typically a toroid or square donut shape and the high current wire simply passes through, forming a one-turn primary). The secondary current is much less, often 5 Amperes at full scale (which might be 100A or more on the main conductor).

enter image description here

The same thing is true of voltages- a 240V input is no problem with reasonable clearances, but a 1kV wire would cause headaches- thick insulation and danger. To solve this problem a potential transformer (also called a voltage transformer (VT) can be used to step the voltage down to something more compatible with instrumentation.

enter image description here

These items are classed as "Instrument Transformers". The operating principles are generally the same as any other transformer, but they are optimized for the intended application.

One interesting quirk is that a CT is typically operated with the output almost shorted so the input current determines the output current, and not the load. If the output load is removed from a current transformer (because the wire breaks, for example), there is quite a bit of transformer core in there (to get good accuracy under normal conditions), so the output voltage can rise enough to be a hazard to someone poking around.



For residential smart meters, every penny is important because of the high volumes, and some use high-current shunts (direct connect) but CTs are not unknown. In the below photo of a North American residential smart meter you can see the two "hot" lines pass through the CT in opposite directions. Since they're 180° out of phase, they add. Since the two hot lines are assumed to be balanced (in voltage), there's no need to measure the neutral current.

enter image description here

Spehro Pefhany
  • 376,485
  • 21
  • 320
  • 842
  • So CT sensors can be clicked onto cables (one on each phase), and is also an easier solution to apply to a house's electrical installation? – Mads Skjern Jan 20 '14 at 15:41
  • See my edit above. There are other options such as Rogowski coils. Cheap is important, and so is making the meters fairly tamperproof, I think both trump installation costs. – Spehro Pefhany Jan 20 '14 at 22:25
  • A very good answer. Especially appreciate the reminder that CT's shouldn't be left open circuit. Always remember your CT shorting links! – Li-aung Yip Jan 21 '14 at 02:54
1

A direct-connected meter has two sets of terminals, one for the line input and the other for the load output. The load current passes through the meter itself. Most residential meters are of this type.

A transformer-connected meter uses external voltage and/or current transformers for sensing and uses relatively light wiring to connect these to the meter itself. Many industrial meters are of this type.

Dave Tweed
  • 168,369
  • 17
  • 228
  • 393