10

I'm a PC software guy, a newbie to electronics. Recently, I've got a project in which I need to source for a DAQ that can provide dry contact inputs to an interfacing digital output controller. The controller generates alarm signals. I've uploaded the system diagram here -

Link to larger image: https://i.stack.imgur.com/KL88h.png

As shown in the diagram, the digital outputs are Form A relays that "are closing contacts with one common terminal (C) and one normally open terminal (NO). The terminals are isolated from signal ground.". So the digital outputs are normally open and I suppose will close only when there's an alarm. It is not indicated in the data sheet whether the digital outputs are wet or dry.

Here's how I figure it will work:

If the digital output relays are open, my dry contacts will not form a circuit. If the digital output relays are close, my dry contacts will become a closed circuit and current will flow because the digital outputs are rated 250VAC/30 VDC, 2A??

But dry contacts are not suppose to have voltage or current? I can't figure how this part works out and will appreciate any pointers. Thank you.

Joshua
  • 235
  • 1
  • 4
  • 8

2 Answers2

4

Dry contact means no energy is supplied to the contacts (completely passive and isolated). In order for the DAQ to read it, it needs to have a defined voltage, Either a pull up to the positive supply (logic 1) or pull down resistors to the negative supply (logic 0) or an additional IO. Usually, DAQs have a reference voltage output, you can use that one, or alternately, an output line, set to a known logic level. Supply voltage is relative to the DAQ supply, either its ground or Vcc. As long as the cable between the alarm and IO board is relatively short, you should not have any problems.

Lior Bilia
  • 7,282
  • 1
  • 20
  • 30
  • Are all digital inputs dry contacts? – Joshua Sep 01 '13 at 06:39
  • No, digital inputs might have a logic level (Due to pull up/down resistors), even when set to input mode. – Lior Bilia Sep 01 '13 at 17:39
  • user2019047's answer is good as well but I' – Joshua Sep 03 '13 at 16:17
  • I'll select yours as the answer. Actually, I still can't visualize it until after until I read this post on NI forum - http://forums.ni.com/t5/LabVIEW/Dry-Contact/m-p/180495/highlight/true#M105155 What this post says is that in order to change the logic to 0, the dry contact must close and ground the circuit. Now I'll need to select the DI module. Would a TTL digital I/O like the following be able to receive a dry contact output? http://www.advantechsg.com.sg/products/USB-4751/mod_5896D86D-DFEB-4B9E-B1C5-A9529A401A5F.aspx# – Joshua Sep 03 '13 at 16:26
0

You wrote: "If the digital output relays are close, my dry contacts will become a closed circuit and current will flow because the digital outputs are rated 250VAC/30 VDC, 2A?? "

Current will not flow because of rated current flow of the contacts. Current will flow because the contacts close a circuit, how much current depends on the circuitry in the I/O DAQ. My guess is very little current, how much will probably be stated in the data sheet for the I/O DAQ.

When the contacts close, the DAQ senses this and reacts accordingly. I assume the dry contacts common (C) are all connected together and connected to a common input on the DAQ, unless the input DAQ channels are all isolated from each other, i.e. each channel requires both contact connections from the dry contacts.

user2019047
  • 166
  • 8
  • Does this mean the digital "output" won't actually supply the output current and voltage? I've been told to source for the input DAQ portion so that part hasn't been decided yet. I'm currently studying LabJack's DAQs, sent them a couple emails and getting more confused with each email. ;) – Joshua Aug 31 '13 at 18:00