Suppose you have a panel. The arc flash incident energy for this panel is computed based largely on the available short-circuit current (SCCA) to the panel, and the protective devices upstream of the panel. Now, if there are current-limiting fuses upstream of the panel, the incident energy should be greatly reduced in many (if not all) cases. Yet SKM Powertools does not account for this phenomenon; the current-limiting behavior of current-limiting fuses is not simulated.
Most of the documentation I'm seeing involves the use of current-limiting fuses to increase the short-circuit current rating (SCCR) of the panel. So for the purpose of computing whether equipment is rated for the SCCA, ignoring the current-limiting behavior is correct, but this has no impact on arc flash incident energy calculations.
Mersen argues that using current-limiting fuses to reduce arc flash energy is valid.
Two IEEE papers seem to agree, though I can't access the full text: https://ieeexplore.ieee.org/document/806456 https://ieeexplore.ieee.org/document/7549099
What is standard industry practice on this subject? Do other simulators besides SKM Powertools account for current-limiting effects? Do engineers do these calculations manually, or is the current-limiting effect ignored for arc-flash purposes? If so, why?
EDIT: Easypower does support computation of arc flash incident energy using current-limiting fuses! At least, it did at the time this video was made:
https://www.easypower.com/resources/article/current-limiting-fuses-in-easypower