Without the DG, the mains goes to, say, 5 flats in my apartment through 5 utility meters.
However, with AMF, the DG is shorted to mains. Wouldn't the utility meters count DG energy too?
Without the DG, the mains goes to, say, 5 flats in my apartment through 5 utility meters.
However, with AMF, the DG is shorted to mains. Wouldn't the utility meters count DG energy too?
Yes, if the utility meters are after the contactors they will record the power used from the generator as well as from the mains.
Since the connections are going to 5 units each with it's own meter there's no easy way around this, but as the generator is only expected to be used on rare occasions the added charges should be negligible.
Also, the generator is not 'shorted to mains', what should happen in a power outage is the contactor from mains is opened and the one from the generator is closed, so one or the other is connected to 'LOAD', they're never actually connected together.