How would I connect a 3 wire RTD using current source and a instrumental amplifier for the output?
UKNP
If you have only one current source it's a little difficult with an inamp because you need a different gain from each input.
For example, in this circuit:
Va = I(RTD + Rlead)
Vb = I(RTD + 2Rlead)
So you could have Vout = 2Va - Vb = I*RTD
What's typically done is to add another matched current source.
simulate this circuit
So Va = I(RTD + 2*Rlead)
Vb = I(2*Rlead)
And Vout = (Va - Vb) = I(RTD)
So you would just connect the instrumentation amplifier inputs to Va (+) and Vb (-)
Of course you could also add a gain of +2 op-amp to the first circuit before the instrumentation amplifier (+) input- an ordinary precision op-amp and two equal-value resistors- which retains the high input impedance of the inamp but adds another active circuit and another source of drift. The two-current source solution is relatively insensitive to matching errors in the left current source if Rlead << RTD resistances.
Spehro Pefhany
  • 376,485
  • 842
Do this: enter image description here Source:
https://electronics.stackexchange.com/q/304817
But instead of using a diff amp, connect the instrumentation amp positive and negative to Vin1 and Vin2.
Voltage Spike
  • 75,799
  • 80