I need a soft start for a ups transformer. Because when I power it with 230v ac it trips the breaker. I need a diagram to build my own soft start circuit.

toolic
  • 5,637
  • 5
  • 20
  • 33

1 Answers1

1

It is all about the inrush current (1, 2). When the primary gets magnetised, the amount of current it needs to build up a magnetic field before collapsing and transferring the energy to the secondary can be 10 times higher than its nominal rating.

An example of an inrush current limiting circuit or a soft starter is the one provided by Steve Gardner but for a Variable Auto-transformer, or Variac