12
I'm specifying cable for a VFD application and came across this table regarding NEC ampacities and corresponding cable size.
table with cable size and corresponding ampacity
What I found interesting is that the ampacity increased with temperature for any environment (Free Air, Single Tray, Conduit). I would have thought that the current would decrease with increasing temperature.
In addition, does this mean at room temperature the current carrying capability would be lower than the ratings @75C and 90C ?
SRR
  • 917
  • 26
    Keep in mind that not just your cable must be rated 90C. Your terminals must be too, as well as the enclosure. For instance 90C is basically off limits for residential work since no consumer-tier panels or terminals are rated 90C. – Harper - Reinstate Monica May 10 '22 at 07:21
    The table mentions temperature rating of insulation, not ambient temperature. Is this for work or hobby? – Roland May 10 '22 at 13:14
You're looking at it from the wrong direction.
The more current you put through a cable, the hotter it gets. Push too much current through, and the insulation starts to deteriorate. Wire insulation, such as PVC or XLPE (cross-linked polyethylene) will have a rated maximum temperature that it can withstand for many years before it starts to deteriorate. Go above that temperature, and the insulation gradually breaks down.
Looking at the top line of the table, if you have a 14AWG cable with insulation rated for a maximum of 75°C, then you can only put 13A through it without damaging the insulation. If you swap it for a cable rated for 90°C, then you can push the current up to 15A.
But be aware that many electrical accessories aren't rated for 90°C, so a very hot wire can also damage the things it's connected to.
JYelton
  • 32,302
  • 134
  • 249
Simon B
  • 18,609
  • 55
    It is worth noting that from the table OP posted, it is not clear what ambient temperature is assumed. If the posted temperatures are deltaT, with an ambient temperature of 25degC you would need insulation capable of withstanding 100degC for 13 A, and 115degC for 15 A. In the likely case that Tamb = 25degC for that table, one must take into account the expected Tamb, which can be a lot higher, especially if you have a 90degC cable in a small box or conduit. – Vladimir Cravero May 11 '22 at 13:17
  • @VladimirCravero Correction factors for ambient temperature can be found in [310.15(B)](https://up.codes/viewer/minnesota/nfpa-70-2020/chapter/3/wiring-methods-and-materials#310.15_(B)). Assumed temperature is generally 40C with exception of single insulated wire in free air (which is 30C per 310.17). – J... May 12 '22 at 01:30
19
Those aren't increases in capacity at higher ambient temperatures, the temperatures are the ratings for the cable.
So if the cable, terminations and equipment in your system are rated for 90 degrees, you use the higher ampacity value, if they're rated at 75 degrees, you use the lower one.
See this page.
GodJihyo
  • 17,628
  • 45
  • For important notes on the impact of terminations on the effective temperature rating, see [110.14(C)](https://up.codes/viewer/minnesota/nfpa-70-2020/chapter/1/general#110.14_(C)) – J... May 12 '22 at 01:39
That's not right. DC resistance of a conductor actually rises with temperature, which means at higher temperatures you will lose more power into heat in the cabling, which will heat it up even more.
The tables just mean that if wire temperature limit is 75 degrees, less current is allowed to pass through it, than in the case of allowing more current until wire heats up to 90 degrees.
Justme
  • 127,425
  • 261
Those numbers you're looking at are established in NEC 310.15(B)(16).
If you had looked at the original source material, and continued to read onward from there, you would have found NEC's treatment of high ambient temperature environments. Which would answer your question.
(They work as you'd expect).
The section you are reading assumes sensible ambient temperatures, and is talking about the thermal rise in wires from ampacity (resistance). It is limiting ampacity so that wires grouped in conduit and/or packed in wall insulation will not exceed their insulation rating, which varies.