Are two-pole breakers required on single-phase 230 V loads when connected to a 3-phase supply with IT earthing system (with distributed neutral) in Germany?
Where in the standards is this requirement specified? What fault would be isolated by a two-pole breaker that wouldn't be isolated by a single-pole breaker?
I'm looking at https://www.se.com/ww/en/download/document/ECT178/ and it says:
Multi-pole breaking, including the neutral conductor when distributed.The reasons for this are:
--breaking only of the faulty phase conductor of a feeder means that three-phase machines are supplied by the two other phases
--breaking of the neutral exposes to phase-to-phase voltage, single-phase loads normally supplied by phase to neutral voltage
The 3-phase load has no neutral, and is protected by a 3-pole breaker, so the first point above is covered
The single-phase loads wouldn't have a breaker on neutral, only on the live phase, so the second point above...doesn't make sense to me.
I'm also about to purchase IEC 60364, but I'm not hopeful that I'll see a cut-and-dry answer in there.
Thanks.