I recently moved to North America, and I was wondering why the houses here seem to be protected by fuses rather than breakers and differential switches like we have in France for example.

It would seem to me like in most cases it would be difficult to reliably/systematically get the Earth loop resistance low enough to allow the fuses to pop when there is a short to an earthed enclosure, and I highly doubt that the fuses are fast enough to protect us against direct electric shock (which differentials do, to some extent).

My guess is that with 120VAC instead of 230VAC, most of the issues become fire hasards due to overloads, and much less electric shock - but I suspect that 120VAC can still be dangerous and lethal in certain situations which are not that rare. Is this why local GFCIs (as in, for a single socket) exist or why I find the sockets here ludicrously dangerous and flimsy compared to all european plugs (my favourite being the UK's)?

Mister Mystère
  • 9,477
  • 6
  • 51
  • 82
  • 16
    My house has breakers, not fuses, and 120VAC split phase service. Breakers and fuses protect against fire (due to wires overheating); GFCI are required for outdoor / wet locations, to protect against electric shock. Think newer construction may be required to use GFCI on all circuits in panel. This is standard in California. What part of North America are you asking about? – MarkU Feb 25 '22 at 23:52
  • Older Canadian houses had fuses, but circuit breakers have been common for many years. There may be some older houses that have not been re-wired that still have fuses, but I expect that the great majority of old fuse boxes have been replaced by breaker panels. – Peter Bennett Feb 25 '22 at 23:54
  • 7
    Old Houses are grandfathered. New houses have to follow state rules and they tend to adopt NEC wholesale. – Passerby Feb 25 '22 at 23:58
  • 20
    Most likely you moved into a very old home that has had the obsolete electrical wiring grandfathered into compliance. Fuses are actually rare, I've lived in old buildings but never seen one still in use. – user1850479 Feb 26 '22 at 01:09
  • 1
    Houses in the US do use GFCI and breakers, only old houses may have fuses and only then of they have old work that has not brought up to code. Asking why us houses use fuses is like asking why they use knob and tube wiring instead of ROMEX; it's just an old standard in an old house that hasn't yet been upgraded. – TimB Feb 26 '22 at 05:59
  • 24
    "*I highly doubt that the fuses are fast enough to protect us against direct electric shock.*" That is not the purpose of fuses. They are to protect wiring and supply against overloads. – Transistor Feb 26 '22 at 12:03
  • From where do you come? In Germany I also often see fuses. – Paŭlo Ebermann Feb 27 '22 at 03:15
  • Many houses in the UK will have a single 50-100A fuse _in addition_ to a breaker panel that protects the entire house, that needs to be replaced by the utility if it blows. – Crazymoomin Feb 27 '22 at 17:29
  • 2
    Breakers aren't inherently faster than fuses. Often slower. – DKNguyen Feb 27 '22 at 20:18
  • Fuse aren’t that common in the US anymore. Almost every house I’ve looked at in the past 20-30 years has had breakers. – RBarryYoung Feb 28 '22 at 17:24
  • 1
    @DKNguyen: Breakers can be designed to trip faster than fuses under certain overload conditions. In general, with a fuse, doubling the current will at best reduce trip time by a factor of four. Breakers, by contrast, can be designed to hold for several seconds at a certain level of current but trip in under 1/30 second at a level 25% beyond that. – supercat Feb 28 '22 at 18:42
  • 6
    An astronomer, a physicist and a mathematician are on a train in Scotland. The astronomer looks out of the window, sees a black sheep standing in a field, and remarks, "How odd. All the sheep in Scotland are black!" "No, no, no!" says the physicist. "Only some Scottish sheep are black." The mathematician rolls his eyes at his companions' muddled thinking and says, "In Scotland, there is at least one sheep, at least one side of which appears to be black from here some of the time. – rrauenza Feb 28 '22 at 19:40
  • I’ve never seen a home wired with fuses in the US. They are incredibly uncommon. – Navin Mar 02 '22 at 12:37

5 Answers5

38

You are mistaken.

There are houses in the US which use circuit breakers - I'd say most of them have circuit breakers rather than fuses.

Houses in Europe aren't all modern and up to date, either.

I know folks in Germany in older houses where they still have fuses.

Many (probably most) American houses have RCD breakers as well, though they are known in the US as ground fault current interrupters (GFCI) instead of residual current devices (RCD.)


Fuses and circuit breakers protect the wiring to prevent fires.

RCDs and GFCIs are there to protect people.

JRE
  • 67,678
  • 8
  • 104
  • 179
  • 5
    And arc fault breakers (AFCI) are very rare in Europe, but somewhat common in USA. – jpa Feb 26 '22 at 16:18
  • @jpa that's probably a side effect of the horrible invention that is the backstab. – Nelson Feb 26 '22 at 17:18
  • 4
    @Nelson: We've got "backstab" outlets in Germany. They work better here because the current is lower. My whole house uses only backstab outlets - I'm not even sure where I'd go to buy ones with screw terminals. – JRE Feb 26 '22 at 19:43
  • 3
    "Houses in Europe aren't all modern and up to date, either." — Case in point: I've lived in 4 houses in the UK, and looked at consumer units in many others, and one of them still used fusewire. [It was this design](https://youtu.be/0L0p5Rk7hZU). – Jivan Pal Feb 26 '22 at 21:05
  • While my apartment itself has breakers, the building (multi-family home) itself has fuses. Poland. – jaskij Feb 27 '22 at 05:33
  • @JivanPal, in the UK, you also often still get [Ring Mains](https://en.wikipedia.org/wiki/Ring_circuit), even with more modern consumer units... – Bruno Mar 01 '22 at 14:34
  • @Bruno Often? Have they been dropped in the last five years? – Martin Bonner supports Monica Mar 01 '22 at 14:52
  • @Bruno I'm aware; my parents' house was originally a two-floor flat when it was built in the 1930s. In 2005, the two old CUs were replaced with two modern ones, new radials/spurs were installed as we wanted extra mains sockets in all rooms, but the old ring main wiring remains unaltered. In particular, the lighting is all still ring mains. – Jivan Pal Mar 01 '22 at 15:05
  • @MartinBonnersupportsMonica I can't remember off the top of my head, but both Radial and Ring were allowed in 17th edition (maybe before) AFAIK. I saw rumours that Rings may have been removed/discouraged in preparation of 18th edition, but that change didn't make it in the final document. That said, you could wire a whole house using radial only (and be compliant). Probably by habit, I've seen electricians installing new cables coming back alongside themselves, just for the sake of having a ring, which kind of defeats the point. (IMHO, their "advantages" don't compensate for their downsides.) – Bruno Mar 01 '22 at 15:07
  • Thanks for the answer. I waited until I saw enough fuse boxes before posting but sounds like I just wasn't lucky. To be honest I may have been biased by the fact I find the plugs extremely dangerous - and just wrongly assumed the rest might follow. Dearest apologies, fellow americans! I voted to close my own question as opinion-based, I hope you will keep the answer scores when it closes. – Mister Mystère Mar 03 '22 at 18:24
35

Our breakers

I would say almost all US homes have breakers. Even those with legacy fuse boxes have breakers between them and the service. There are six major types of service panel, and all 6 designs were settled in the 1960s. I have a 1960 CH panel that takes modern CH breakers. This video represents our standard layout (except the 240V breakers on that "QO" type have only a single handle, oddly.)*

Some older houses still have fuse boxes for lighting. This is because in the past, they did only a partial re-wire, and left the original fuse box in-place to feed typically lighting circuits. It is wired as a "subpanel" fed from a breaker in the new circuit breaker panel. We have that in this 1924 home.

The USA is a 240V country actually; we just use a center-tap to get half voltage for small circuits. The above video explains it all. **

It would seem to me like in most cases it would be difficult to reliably/systematically get the Earth loop resistance low enough to allow the fuses to pop when there is a short to an earthed enclosure.

Actually no. Earthing has been required starting in the 1950s and on all circuits (except dryers and ranges) since 1966. Further, USA earth wires are always the same size as the live conductors up to 30A; we don't shrink earth like Europe does, until you get to 40A or larger. Even then, Code calls out a minimum size for earth to assure it can clear faults (trip breaker).

Also up to 30A, we limit wires to their ampacity at 60°C thermal. For instance our 14 AWG (2.1mm2) is only allowed 15A breaker (and most appliances also have an 80% derate, so for instance a 30A dryer or water heater does not exceed 24A draw, and most plug-in appliances with 15A plugs don't exceed 12A.)

My guess is that with 120VAC instead of 230VAC, most of the issues become fire hazards due to overloads, and much less electric shock - but I suspect that 120VAC can still be dangerous and lethal in certain situations which are not that rare. Is this why local GFCIs (as in, for a single socket) exist or why I find the sockets here ludicrously dangerous compared to most European plugs?

120V vs 240V is slightly less dangerous to humans. It probably makes a bigger difference in equipment and wiring faults due to Ohm's Law. (Double the voltage double the current; thus 4x the power).

Note that although the US is a 240V country, nothing is more than 120V to earth. This an approach the British took with construction-site 110V power, where each "leg" is 55V to earth.

We are concerned with series arc faults (arcing across a loose connection in series with the load) more than Europe is; since our 120V appliances take twice the current for the same job, series arcing makes twice the heat.

European power is distributed to the poletop as 3-phase 400V "wye" with 230V phase-neutral. 1 to 3 phases are delivered to each home.

If you add 20% to that, consider what you get: 480V 3-phase with 277V phase-neutral. That is exactly what USA industrial power is. Culturally, it is treated with fear and respect - here's a 277/480V arc flash... Electricians are not as quick to work "live" in a 277/480V panel. The major difference is the presence of "whole-house RCD" to protect most parts of the system in a European house.


* Normally our 240V breakers appear like two singles handle-tied. They aren't. Actually there's an internal mechanism for "common trip", the handle ties are merely decoration / to remind a maintainer that both must be thrown.

** Originally, 120V (well, 100V then) was only for lighting and 200V for everything else. But then, they provided receptacles/sockets for desk and floor lamps, and then people plugged radios into them, and then things got out of hand. We have a 240V plug standard (NEMA 2 and NEMA 6); we really ought to start using it so we can have fast kettles.

GFCI vs RCD

In Europe, they use a "whole house RCD" to detect leakage currents (current drawn by house does not match current returning). This is a compromise system with a number of priorities: detect ground faults that threaten equipment, provide limited personnel protection, stop parallel arc faults (arcing live-earth or neutral-earth that is not sufficient to trip an overcurrent fuse or breaker), and do this economically at a whole-house level. The technology at the time favored RCD, as digital signal processing was not yet ready.

The ideal detection threshold for human protection is 5 mA of leakage. However, a whole house has ordinary current leakage that is not a threat and is unavoidable (not least: electrical cables have capacitance) which is higher than that. Europeans and Americans took different tacks to this dilemma.

In Europe, the opportunity to protect the whole house was seen as worth exchanging for somewhat less human protection. So a 30 mA threshold was chosen.

The United States came around slowly, and placed human protection first. As such, "5 mA threshold" was not negotiable, and they traded away the opportunity to protect the whole house.*** So the protection is applied on a per-circuit basis with some length limitations. And this results in most circuits not being protected, except on the most modern houses where most circuits are protected by use of many xFCI breakers.

When the U.S. finally came around to dealing with arc faults, more modern tech was available, such as digital signal processors to actually "listen to" the electrical waveform on the wire for the pattern ("sound") of arc faults. That crinkle-crunch sound you get hooking up speakers live is the sound of an arc fault. Most of those AFCIs include RCD/GF detection as a way detect L-E and N-E parallel arc faults. However they use the 30mA sensitivity.


*** Keep in mind, American services are enormous. A typical main breaker is 200A on a single (split) phase. Compare with a German home with 64A main breaker x 3 phases. But you can see where an RCD detect coil with 3-wire 200A going through it would be a beast. It probably wouldn't fit in any of our breaker casings!

Our sockets

For those who fear our sockets, placing the circuit under GFCI protection is a near "golden bullet" for this problem and many others. You can also enhance safety by installing the sockets ground up, so if a metal thing falls in the gap, it will land on the ground first. (Assuring contact with it and any other pin will result in immediate GFCI trip).

Remember our GFCIs are 5mA-rated for full human safety protection, unlike the 30mA compromise system used in 230V-land. 10mA can stun, and a stun is a kill if water or ladders are involved.

The UK plug is a handful, and while the fuse is nice, our appliances are rated by UL to fail reasonably, i.e. trip any circuit breaker they're allowed on before bursting into flame. This is also why using the correct breaker is required; if Article 230 motor rules allow a 35A breaker on a 16A motor load but UL says only 25, it is because UL believes a 30A breaker would not trip soon enough.

  • Does that make U.S. wiring _safer_ in the GFCI/RCD department, due to the lower trip threshold? – Vikki Feb 26 '22 at 19:09
  • 4
    @Vikki Yes, less dangerous :), but only on the circuits which are protected. – Harper - Reinstate Monica Feb 26 '22 at 19:23
  • Curious, why would a "RCD detect coil with 3-wire 200A" be a beast? Is it not only as large as the *smallest* current that needs to be measured? – P2000 Feb 27 '22 at 06:01
  • 2
    @P2000 Hmm, I assume the current goes through a few loops to increase sensitivity. If not, then maybe, but three 2/0 copper is still a fat bundle. – Harper - Reinstate Monica Feb 27 '22 at 06:32
  • 2
    I don't know about the rest of Europe, but here in the UK using a single RCD for the whole house is frowned upon, at least two is more common. – Peter Green Feb 27 '22 at 08:46
  • Ah ok, yes the three 2/0. I thought you suggested the RCO was going to be fat. – P2000 Feb 27 '22 at 15:29
  • Very interesting, thanks! I waited until I saw enough fuse boxes before posting but sounds like I just wasn't lucky. To be honest I may have been biased by the fact I find the plugs extremely dangerous - and just wrongly assumed the rest might follow. Dearest apologies, fellow americans! I voted to close my own question as opinion-based, I hope you will keep the answer scores when it closes. – Mister Mystère Mar 02 '22 at 20:39
  • 1
    @MisterMystère I don't think it's opinion based, it's a valid question with valid answers of how Americans went to great lengths to make the system safe, [or abjectly failed to](https://www.youtube.com/watch?v=K_q-xnYRugQ). (and how we have been dragged down by legacy standards which we set quite early, such as split-phase which goes clear back to Edison). – Harper - Reinstate Monica Mar 02 '22 at 21:52
14

There are houses in the US that use fuses, because they had electricity installed in the first half of the 20th century, and the electrical system hasn’t been upgraded/replaced since then. Those are the only homes that use fuses, and the reason they have fuses is historical.

If you have seen such a house in person, or if you live in one, then the reason it has fuses is that the landlord is a penny pincher and never invested in bringing the house into at least the 2nd half of the last century in terms of the electrical system. A lot of “investment” properties like that, i.e. rental properties, are badly neglected and only the minimum is done to maintain them. That’s typical of many older university campus areas for sure.

9

Early household systems (late 1800s until the mid-1930s) used fuses. This same era also used ‘knob and tube’ wiring. Both are long obsolete, in North America and elsewhere.

Nonmetallic Sheathed Cable (NM Cable, aka ‘Romex’) came in to use in mid 1920s (introduced 1922, added to NEC codes c. 1926.) Knob and tube persisted until the postwar era, when it was finally banned by code for all new and retrofit construction.

I mention knob and tube and NM cable because replacing knob and tube is one of the reasons fuses get swapped for breakers as a retrofit.

Breakers came to houses later than NM cable. Although they were invented in the early 1900s and used in commercial systems, they didn’t see use in household wiring until later - mid 1930s.

As for fuses being an ‘American’ thing, nope. There are still old houses all over the world with fuse boxes, and some even with knob and tube.

It’s fair to ask, are these old systems more common in the US than elsewhere? Maybe, for several reasons.

Electricity was introduced in North America earlier than in Europe. This coincided with the Gilded Age construction boom, the result being large population of then-new and refitted houses using knob and tube systems with fuses.

Because we have so many of these old homes, US and Canadian standards are (probably) more lax than in the EU, because freedumb and all that. NEC and local codes allow old systems to be ‘grandfathered in’ as long as they’re in working order, even today, more than a century after they were built. There’s no forced retrofit when a home is sold. There is incentive however, more about that below.

Finally, we haven’t had two devastating wars destroy our buildings, so more of these old systems remain.

Regardless, breaker panels and Romex for new and retrofit have been the norm for houses built after WWII. They’re required by code.

Related: https://www.quora.com/What-year-did-knob-and-tube-wiring-stop

Why get rid of knob and tube?

Knob and tube systems have a number of issues:

  • no grounding
  • Limited amps capacity
  • Failing solder joints
  • Crumbling insulation
  • Added building insulation affects performance: wires can overheat

For these reasons, insurance companies consider knob and tube a fire risk. They will either refuse to write a policy on a house or charge higher premiums.

So there is considerable pressure to upgrade historical homes to modern wiring, even if code still allows the old systems. And when that retrofit happens, the service usually gets upgraded to more amps, brought by a new feed to a modern breaker panel, as required by code. Any remaining knob and tube wiring is on its own junction box.

hacktastical
  • 49,832
  • 2
  • 47
  • 138
  • I think you are confusing the question of when certain wiring devices first appeared on the market with the question of when they took over. From what I have seen in New England, knob and tube was used in the first part of the 20th century, then BX cable with fuses in the middle of the century, then NM with fuses in the 1960's. Circuit breakers with NM were standard in residential construction by the 1980's. I'm pretty sure the reason they finally pushed out fuses was dropping cost due to cheap manufacturing in Asia. – David42 Mar 01 '22 at 15:59
  • Building codes combined with increased power demand in residences rendered fuse boxes obsolete shortly after WWII ended. – hacktastical Apr 20 '22 at 14:24
3

Not directly relevant, but I'd like to address the fallacy that breakers are inherently safer. Which I also used to believe was true until I spent some time studying how domestic electrical systems work (in the UK).

Fuses and circuit breakers are overcurrent devices. Since a fatal shock is far below the normal current draw an appliance may have, there is no way they can protect against direct contact with a live wire. They protect against overload. Neither fuses nor breakers are sensitive enough to trip instantly at moderate overloads and in some cases, fuses (e.g. ceramic fuses, especially the BS1361 type) are actually more sensitive than the breakers that tend to be used for the same application in some conditions and usually have a higher breaking capacity too (which may be why modern UK installations with circuit breakers also have an electricity company-owned BS1361 fuse on the main incoming cable). Re-wireable fuses are generally less sensitive, but not inherently unsafe as you might (in fact UK regulations insist on) just using them with a thicker circuit cable to compensate.

The main issue is that fuses can be replaced with the wrong rating of fuse, or with a nail or foil, whereas breakers are less subject to this kind of user error.

While fuses do not protect against direct contact with a phase/live/hot wire, if an appliance is earthed (grounded, as the US terminology goes) then the user is to some degree protected from touching a live (US = hot) metal casing as the fault causes a massive overload which blows the fuse.

To protect against direct contact with a live wire, RCDs are essential (though as others have said, the typical 30mA rating used in Europe may not always be sensitive enough). It is worth noting that Residual Current Devices are magnetic devices that sense an inbalance between the current flowing down the live and that returning along the neutral of a European circuit. We used to use ELCBs (Earth Leakage Circuit Breakers) which are not quite the same thing as while they will only detect current if it is leaking back via the earth (ground) cable. ELCBs may offer some protection if you have one hand on earth-bonded metal and the other on a live wire, but they would not offer any protection if you had one hand on the wet soil in the garden instead of on the grounded metal. Which is why we no longer install such devices.

Obviously, an old installation with fuses is unlikely to contain an RCD, so there is a very obvious correlation between safety and having modern breakers, but it is not actually the lack of breakers (we call them MCBs in the UK) but, rather, the lack of an RCD that is the problem.