I have a GFCI socket in a recently-build bathroom. My hair trimmer trips it often when stopping under some conditions and while I have a fix I'd like to better understand what exactly is going on here.
I need an extension cord to use my hair trimmer inside the bath (not to use it with the shower, just to collect the hair...), and the issue was when using the extension. I could fix it with an AC capacitor... so let's start with the setup:
The trimmer is an Andis PM-1 pivot-motor marked with the following specs: 12W 120V 60Hz. It has a ~220cm cord of unknown gauge (outer shell is 5.8mm, round, flexible so I presume stranded copper).
The extension cord is ~305cm long, hand-made from fairly thick lamp wire (the kind that has two visible wires that can be teared apart). It's likely 14AWG; I measured single strands at 0.28mm and counted 26 of them. Plugs on both ends are rated 15A 125V (peak? I hardly think this is sustained rating but it doesn't say).
The cap used is a film capacitor marked .47µF 275V, type MKP (I can provide full markings and even a photo if needed), salvaged from a dead laptop adapter.
The issue
I actually didn't realize the extension was the issue until I started testing with the capacitor... So:
With no ext cord, the GFCI never trips.
With the extension cord, the GFCI trips often on stop, likely depending on motor position. I presume the current feedback is higher if the motor's rotation isn't stopped early by the blade reversing.
With the cap at the trimmer cord / extension junction the GFCI never trips.
The cap has no effect if connected directly on the GFCI socket.
The questions
I understand AC motors cause a shift between current and load and that can be problematic... and also that they can have a very high power draw on start and feed it back on stop causing a surge (correct me if I'm inexact or even plain wrong here...)
Based on that I understand the GFCI could be seeing this as an earth leak, though since it's only on stop and that should be feeding current back in, that's kind of the opposite of a "leak".
Therefore I'm wondering about the following:
Why is the GFCI actually tripping? Are my assumption correct? Is is only detecting differential (meaning leak or feeding current back both cause it to trip the same way)?
What makes it only happen when using the power cord?
I tried using the cap because that's what used on large-scale motors to correct power factor, though I'm not even sure it's the right cap for the job (after looking it seems to be used for EMI filtering...). It is actually correcting PF / absorbing the off surge, or something else is happening here?
4. (if not answered previously) Why the cap has no effect on the GFCI end?
Update:
The original issue no longer appears after is almost impossible to reproduce since I rewired the socket-end of the extension (male plug), despites that the connection looked pretty strong before (5-6 strand were broken, new connections have no more than 1-2 broken strand and does a longer loop around the screws). It also work (doesn't trip) with the cap on the socket end but I'm unsure if I somehow misconnected the alligator clips in my earlier tests or if it was just helping a bit (I didn't analize precisely fail rate, just noted whenever it failed at all).
I can still trip the GFCI by pulling any plug directly with the trimmer turned on as long as the cap isn't connected somewhere, although this may be an entirely different issue; the extension isn't even needed for that. If the cap is connected, it doesn't trip no matter which plug I pull or whenever the cap is before or after the plug I pull. It even works (doesn't trip) if I connect the capacitor on the other socket of that GFCI (I remember that was the first way I tried to connect the cap and it didn't work, then I tried between the ext. cord and trimmer as it was easier than connecting on the socket side).
If that may be meaningful, my earlier tests were with the cap connected using very cheap alligator wires (always the same wires though, moving the whole setup) connected directly on the plug prongs with the plugs halfway in. I have since then soldered it inside a ground plug adaptor with the ground pin removed & hole filled with epoxy (no wires or risk of a bad manual clip connection and plugs fully inserted when testing now).