I understand you want to design this as a three phase inverter, but it looks like your main question is how to make the output less distorted. So, from this perspective, as I mentioned in the comments, the output will be influenced by the control loop. For example, here is a basic half-bridge with a pure voltage mode loop, involving a simple PI filter:
V4
is the reference signal, G3, C2
form the loop filter, G4
is the equivalent of a resistive divider voltage feedback, E1
inverts the signal, A1, A2
are comparators for the SPWM, G1, R1, G2, R2
pose as drivers. Instead of V2, V3
you can have a single supply and split capacitors; about the same thing (except different grounding). Here, as it is it's a bit more convenient for the voltage feedback. There's no dead-time, I know.
I kept your values, but a few things to notice: the triangle has a DC that transforms it from bipolar to unipolar, the comparators will need to deal with the negative voltage swing at the input (even if the output will be from 0 to Vcc), and the compensation is done very lazily and without any concern for stability (which you will have if you want bandwidth). For this last reason, the output waveform (blue) is slightly triangular, because the bandwidth is quite reduced. You can see that the error voltage (black) compensates for the distortion. Without a loop you'd be getting the waveforms you have already seen. More bandwidth will get you better waveforms, but also get closer to instability.
For a three phase simply add two more legs (6 transistors in total). You should know that, in general, 3-phase inverters don't consider each phase in particular, but together, through the help of Clarke or Park transformations. This makes it easier to control the outputs, and also adds the possibility of having the inverter act as an active power filter (thus mitigating the imbalance). Also, for "a few kW" you may need to tone down the switching frequency, unless you're willing to spend more for GaN transistors (you'll be switching ~10 A at high voltage!). Not lastly, while the control could be made analogic (it has been done, with great care and maybe even stable results), the way to go is with a microcontroller.
Here is the code, save it as a file with the extension .asc
Version 4
SHEET 1 1244 680
WIRE 1120 -96 736 -96
WIRE 736 -64 736 -96
WIRE 1120 -64 1120 -96
WIRE 624 16 560 16
WIRE 688 16 624 16
WIRE 0 32 -80 32
WIRE 112 32 48 32
WIRE 176 32 112 32
WIRE 208 32 176 32
WIRE 272 32 208 32
WIRE 384 32 272 32
WIRE 512 32 448 32
WIRE 0 48 0 32
WIRE 384 64 336 64
WIRE 624 96 560 96
WIRE 736 96 736 32
WIRE 736 96 624 96
WIRE 784 96 736 96
WIRE 896 96 864 96
WIRE 960 96 896 96
WIRE 992 96 960 96
WIRE 1120 96 1120 16
WIRE 1120 96 1072 96
WIRE 1152 96 1120 96
WIRE 1152 112 1152 96
WIRE 736 176 736 96
WIRE 1120 176 1120 96
WIRE 624 256 560 256
WIRE 688 256 624 256
WIRE 384 272 256 272
WIRE 512 272 448 272
WIRE 208 288 208 32
WIRE 336 304 336 64
WIRE 384 304 336 304
WIRE 624 336 560 336
WIRE 736 336 736 272
WIRE 736 336 624 336
WIRE 1120 336 1120 256
WIRE 1120 336 736 336
WIRE 336 368 336 304
WIRE 176 432 176 32
WIRE 960 496 960 96
WIRE 960 496 224 496
FLAG 336 448 0
FLAG -80 112 0
FLAG 512 80 0
FLAG 512 320 0
FLAG 1152 112 0
FLAG 896 160 0
FLAG 208 336 0
FLAG 256 352 0
FLAG 0 96 0
FLAG 48 112 0
FLAG 112 96 0
FLAG 224 448 0
FLAG 176 512 0
FLAG 272 32 err
SYMBOL voltage 336 352 R0
SYMATTR InstName V1
SYMATTR Value pulse 0 10 0 25u 25u 0 50u
SYMBOL Digital\\diffschmitt 384 -16 R0
WINDOW 3 -20 -9 Left 2
SYMATTR Value vt=0 vh=0 tau=25n tripdt=25n
SYMATTR InstName A1
SYMBOL nmos 688 -64 R0
SYMATTR InstName M1
SYMATTR Value STW11NM80
SYMBOL g 560 0 R0
WINDOW 0 0 3 Left 2
WINDOW 3 6 116 Left 2
SYMATTR InstName G1
SYMATTR Value 1
SYMBOL res 608 0 R0
SYMATTR InstName R1
SYMATTR Value 12
SYMBOL nmos 688 176 R0
SYMATTR InstName M2
SYMBOL g 560 240 R0
WINDOW 0 21 1 Left 2
WINDOW 3 27 112 Left 2
SYMATTR InstName G2
SYMATTR Value 1
SYMBOL res 608 240 R0
SYMATTR InstName R2
SYMATTR Value 12
SYMBOL voltage 1120 -80 R0
SYMATTR InstName V2
SYMATTR Value 300
SYMBOL voltage 1120 160 R0
SYMATTR InstName V3
SYMATTR Value 300
SYMBOL res 976 112 R270
WINDOW 0 32 56 VTop 2
WINDOW 3 0 56 VBottom 2
SYMATTR InstName R3
SYMATTR Value 32
SYMBOL ind 768 112 R270
WINDOW 3 5 56 VBottom 2
SYMATTR InstName L1
SYMATTR Value 2m
SYMBOL cap 880 96 R0
SYMATTR InstName C1
SYMATTR Value 10u
SYMBOL voltage -80 16 R0
WINDOW 0 21 100 Left 2
WINDOW 3 -12 126 Left 2
SYMATTR InstName V4
SYMATTR Value sin 0 10 50
SYMBOL e 256 256 R0
WINDOW 0 37 29 Left 2
SYMATTR InstName E1
SYMATTR Value -1
SYMBOL g 48 16 R0
WINDOW 0 20 91 Left 2
WINDOW 3 29 119 Left 2
SYMATTR InstName G3
SYMATTR Value 1
SYMBOL cap 96 32 R0
WINDOW 0 26 17 Left 2
WINDOW 3 -35 -35 Left 2
SYMATTR InstName C2
SYMATTR Value 1m rser=10 rpar=1g
SYMBOL g 176 416 M0
SYMATTR InstName G4
SYMATTR Value 40m
SYMBOL Digital\\diffschmitt 384 224 R0
SYMATTR InstName A2
TEXT 400 -128 Left 2 !.tran 40m uic
TEXT 392 -96 Left 2 !.save v(err) i(r3)