On electrical schematics, is there a standard for whether there is a space between the numerical value and unit symbol? I can find standards that require it in general writing, but none that specifically address it for electrical schematics. Sometimes space is at a premium, e.g. 5A
might fit within a circuit breaker symbol where 15 A
would not, so that's the reason I could see that spaces are not required in schematics.
NIST succinctly summarizes the requirement for writing, which comes from section 7.2 of the NIST Guide for the Use of the International System of Units (SI) states
There is a space between the numerical value and unit symbol...
The International System of Units (SI) prescribes in section 5.4.3:
The numerical value always precedes the unit and a space is always used to separate the unit from the number.
ISO 1219-2:2012 for pneumatic/hydraulic schematics uses a space in almost all their examples, but page 39 does also show 0.03cm³/stroke
without spaces.
I have access to and checked UL 489 (Apr 22, 2019) and UL 508A (Apr 24, 2018), but they do not address units directly and do not have example schematics, either.
Edit: And our own Electrical Engineering Stack Exchange Rules and guidelines for drawing good schematics also omit spaces, but those examples are for PCBs rather than electrical panels which is what I'm looking at.