Note: "Ground loop" in this question refers to a ground loop caused by linked magnetic fields. (Sometimes ground loop refers to slightly different scenarios.)
Recently I've been looking into ground loops a lot since I've encountered them in circuits I've set up. I've been trying to analyse ground loops using circuit theory to understand why they happen and how to fix them, however my analysis produces results opposite to what is suggested by Wikipedia (as of 14/09/2021) and many pages on the internet. Where am I wrong?
Below is a schematic of a typical ground loop situation, with mesh currents \$i_s\$ and \$i_g\$ circulating around their respective loops. \$R_L\$ models the input impedance to some amplifier/oscilloscope/multimeter/etc. We can assume that the contents of the two boxes are unaffected by any EMI in the environment (maybe they connect off via twisted pairs far, far away). The signal that will end up getting amplified/read will be \$i_s R_L\$. Diagram of ground loop model In the above diagram: the top wire is the signal wire, the middle wire is the signal cable's ground shield, and the bottom wire is the ground connection via the mains wiring.
Each bit of conductor has some resistance, modelled as \$R_1\$ and \$R_2\$. We assume that \$R_L\gg R_1\$ and \$R_L\gg R_2\$ (the amplifier has a high input impedance, say a few megaohms - way higher than any resistance the wires might have). The loops of wire will also have some self-inductance - but we will model that directly using Faraday's law later on. Note that I didn't include any resistance in the top signal wire - this is because it is negligible compared to \$R_L\$ which it is in series with.
Finally, we assume that the area of the loop for \$i_s\$ is negligible compared to the area for \$i_g\$ (you could imagine that the signal and ground wires overlap exactly, or are a twisted pair).
Now we can solve for the loop currents using mesh analysis. For the ground loop, we will just apply Faraday's law directly rather than trying to include the parasitic mutual and self inductances into the model so that we can use KVL. For the signal loop, there is no linked flux per our previous assumption, which means Faraday's law just simplifies to KVL around the loop: $$ v_s-i_sR_L-(i_s-i_g)R_1=0\tag{1} $$ For the ground loop, we assume that it links a magnetic flux caused by EMI in the environment and by the loop's own magnetic field, which is proportional to the current flowing around it (this is the loop's self inductance). By Faraday's law, we get an EMF around the loop equal to: $$ \oint_\text{clockwise ground loop}\mathbf{E}\cdot d\mathbf{l}=-\frac{d\Phi_\text{total}}{dt}=-\frac{d}{dt}(\Phi_\text{noise}+Li_g)=-\frac{d\Phi_\text{noise}}{dt}-L\frac{di_g}{dt} $$ We will call the noise term \$v_n\$ - it's sort of like a voltage source is distributed around the loop. Thus: $$ \oint_\text{clockwise ground loop}\mathbf{E}\cdot d\mathbf{l}=v_n-L\frac{di_g}{dt} $$
Ohm's law can be stated more generally as: $$ \int_\text{resistor}\mathbf{E}\cdot d\mathbf{l}=iR $$ Thus, we can split the closed loop integral into integrals over each resistance. This gives: $$ (i_g-i_s)R_1+i_gR_2=v_n-L\frac{di_g}{dt}\tag{2} $$ Now we have the two loop equations, equation 1 and equation 2. There's a derivative in there, which is a bit annoying (makes the whole thing a first order ODE in \$i_g\$). However, we can just take this to the Laplace domain to turn it into an algebra problem. (If you're not used to the Laplace transform, \$sL\$ is essentially the same as \$j\omega L\$ used for phasors.) $$ V_s-I_sR_L-(I_s-I_g)R_1=0\tag{1a} $$ $$ (I_g-I_s)R_1+I_gR_2=V_n-sLI_g\tag{2a} $$ Solving equation 2a for \$I_g\$ gives us: $$ I_g = \frac{V_n+I_sR_1}{R_1+R_2+sL} $$ Substituting this into equation 1a gives us: $$ \begin{align*} V_s-I_sR_L-I_sR_1+I_gR_1&=0\\ V_s-I_sR_L-I_sR_1+\left(\frac{V_n+I_sR_1}{R_1+R_2+sL}\right)R_1&=0\\ V_s-I_sR_L-I_sR_1+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n+\left(\frac{R_1}{R_1+R_2+sL}\right)I_sR_1&=0 \end{align*} $$ $$ \begin{align*} V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n&=I_sR_L+I_sR_1-\left(\frac{R_1}{R_1+R_2+sL}\right)I_sR_1\\ V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n&=\left(R_L+R_1-\left(\frac{R_1}{R_1+R_2+sL}\right)R_1\right)I_s \end{align*} $$ Therefore: $$ I_s=\frac{V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n}{R_L+R_1-\left(\frac{R_1}{R_1+R_2+sL}\right)R_1} $$ The signal that we read will be equal to \$I_sR_L\$. Thus, we multiply by \$R_L\$ to get: $$ V_L=I_sR_L=\frac{V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n}{R_L+R_1-\left(\frac{R_1}{R_1+R_2+sL}\right)R_1}\cdot R_L $$ We can apply some algebra to finesse the denominator into the following: $$ V_L=\frac{V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n}{R_L+\frac{(R_1)(R_2+sL)}{R_1+R_2+sL}}\cdot R_L $$ The fraction in the denominator is just the impedance of \$R_1\$ in parallel with \$R_2+sL\$, which can be notated as: $$ V_L=\frac{V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n}{R_L+(R_1)||(R_2+sL)}\cdot R_L\tag{3} $$ Now, since we assumed that \$R_L\gg R_1\$ and \$R_L\gg R_2\$, the denominator is approximately equal to \$R_L\$, which gives: $$ V_L\approx\frac{V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n}{R_L}\cdot R_L $$ This gives our final expression for \$V_L\$: $$ V_L=V_s+\left(\frac{R_1}{R_1+R_2+sL}\right)V_n $$ But this doesn't match what Wikipedia says about ground loops. The above equation implies that increasing \$R_1\$ will make the noise worse, not better. However, the Wikipedia page suggests putting a 10 ohm resistor on the ground shield of the signal cable to mitigate ground loops, but this equation suggests that doing that should increase the noise seen at the load!
Furthermore, we can take the limit as \$R_1\rightarrow\infty\$, which models the case of an open circuit. To do this, we should use equation 3 (which is before we approximated that \$R_L\gg R_1\$). Taking equation 3 to the limit of \$R_1\rightarrow\infty\$ gives us: $$ V_L=(V_s+V_n)\frac{R_L}{R_L+R_2+sL} $$ This implies that you would see the full noise of the loop, except scaled down by a voltage divider (which would have approximately unity gain if \$R_L\$ was very large). And this even makes sense if you look at the circuit without the middle ground path in it!!! However, this contradicts common practice (according to the internet), where a "ground lift" is often used to mitigate ground loops by open circuiting the ground shield of the signal wire.
Furthermore, if you open circuit \$R_2\$, you get: $$ V_L=V_s\frac{R_L}{R_L+R_1} $$ which is similar to before, except with a slightly different voltage divider and no noise. If \$R_L\$ is very large, we get \$V_L=V_s\$.
What's going on here? Why does this analysis seem to indicate that much of the internet is wrong about how to mitigate ground loops? In fact, I could even argue that the above result makes sense. People say that putting resistance in there prevents the ground loop currents from flowing. But who cares about current! We care about voltage (if the input impedance of the load is very high, it is basically just a voltmeter). While increasing \$R_1\$ makes it harder for current to flow overall, it increases the coupling between the loops for \$I_s\$ and \$I_g\$.
Help! Either there is an error in my calculations (which I doubt would affect the final answer, since the final answer makes intuitive sense to some degree). More likely is that I am missing something important in the model. A core assumption is wrong.
PersonWithName
  • 473
    Get hold of a freely available and free simulator and check your results in that. – Andy aka Sep 12 '21 at 09:46
  • Hi Andy, I have experimentally verified my results. See my posted answer. I am not able to determine why the internet disagrees though. I'll double check in a circuit simulator, but that will only catch errors in my algebra, not errors in my model (I have to get the correct lumped element model in the simulation for it to work). However, given that my experimental results match the analysis, I am even more sure that the analysis is correct. – PersonWithName Sep 12 '21 at 10:04
  • Hi @Andyaka - I have simulated this circuit lab and the results are exactly as what my conclusions would expect. Open circuiting the ground shield (\$R_1\$) causes maximum noise at the load, whereas open circuiting the ground loop (\$R_2\$) causes no noise. Not open circuiting either produces a result with some attenuated noise. This contradicts the internet, which says that ground lifts mitigate ground loop! – PersonWithName Sep 12 '21 at 10:25
  • In fact, the results of this analysis seem intuitively obvious. If you open circuit the ground shield, the big loop which acts as a voltage source for the induced noise is now in series with the signal. If you have a low impedance ground shield however, this will short across this big loop and reduce the noise. – PersonWithName Sep 12 '21 at 10:26
  • So, why are you saying this in your question: *Why does this analysis not match the real world?*? – Andy aka Sep 12 '21 at 10:29
  • Initially I misinterpreted my experimental results and believed that to be the case, hence why I wrote that. However, now my experiment seems to indicate that it does match the real world, but it does not match what many pages on internet say (including many pages cited by Wikipedia). – PersonWithName Sep 12 '21 at 10:32
  • I have edited the question to remove mentions of the analysis not matching my own experiments. Either the entire internet is wrong, or there is something wrong with my experiments, analysis and simulations.... – PersonWithName Sep 12 '21 at 10:35
  • _"my analysis produces results opposite to what is suggested by Wikipedia and **the rest** of the internet.... Either the **entire** internet is wrong, or..."_ - Fallacy of the excluded middle. We all know that _some_ of the internet is wrong, but even [Wikipedia's own entry on ground lift](https://en.wikipedia.org/wiki/Ground_lift) (top Google search for me) doesn't exactly sing its praises. Other top Googles search results such as [ePanoram.net](https://www.epanorama.net/documents/groundloop/groundlift.html) have similar caveats about the practice. – Bruce Abbott Sep 14 '21 at 00:58
    Yeah I was a little melodramatic. I saw Wikipedia's article on ground lifts recently, which was actually quite reasonable since it focused more on balanced lines - which is a case where I now believe ground lifts can make sense. But there definitely is a lot of misconception and bad explanations out there. I edited the question to tone it down a bit. - But see my answer, I believe that the internet is right that ground lifts can be useful in some scenarios, but some misconceptions have spread about why they are useful and how they work. – PersonWithName Sep 14 '21 at 02:39
  • That [ePanorama.net](https://www.epanorama.net/documents/groundloop/groundlift.html) link you provided did give some important caveats. But it still contained a few things that I now believe to be misconceptions. E.g., it implies that putting resistors in there fixes ground hum by "reducing the current". This is not true. Current is not the problem (except to the extent that it may cause ground wiring to have their current ratings exceeded). As far as signal is concerned - voltage is the problem. In most circuits, increasing a resistance will *increase* the voltage drop, not decrease it. – PersonWithName Sep 14 '21 at 03:02
    I've worked with a lot of equipment that had ground lifts, and can't remember a single instance when they were helpful. The resolution is *always* to correct the ground fault. – Robert Harvey Sep 17 '21 at 13:30
  • Have you peeked at Horowitz and Hill's very nice chapter on this? – Scott Seidman Sep 17 '21 at 14:47
  • I had a read of section 8.16 (Interference, shielding, and grounding). Great book! Some observations: (a) Fig 8.127 shows that a differential receiver allows the receiving end of the shield to be ungrounded without issues - however this differs from my interpretation of "ground lift" in this question since I assumed it to mean a completely disconnected shield, rather than running it into a differential receiver. (b) Fig 8.131 shows a similar scenario, but on the sending end. The ground shield on the sending end is still connected, which differs from the case I've analyzed. – PersonWithName Sep 17 '21 at 16:38
  • Section 8.16.2 talks about "currents that ... are flowing through a ground line ... can generate a signal" seems to be talking about common-impedance coupling rather an induced ground loop. This chapter definitely helped though. I'm taking away that "ground lift" is a little ambiguous. The misconceptions on the internet probably come down to a few bad diagrams floating around with single-ended receivers having the shields completely disconnected (which is what I've taken "ground lift" to mean for the purposes of this question). – PersonWithName Sep 17 '21 at 16:45
  • So "ground lift" per se isn't really what I have a problem with. It's the specific form of "ground lift" depicted online and the bad argumentation behind it (e.g., "it stops the current flowing, therefore no noise!!!"). – PersonWithName Sep 17 '21 at 16:46
Note: When I use the term "ground lift" I am referring to when the ground of one end of a signal cable is disconnected. The term applies to other scenarios too, such as a ground lift switch that isolates the primary and secondary windings of an isolation transformer or other types of isolators, or a (probably dangerous) cheater plug.
I have come to the conclusion that my analysis was correct given the assumptions. I was able to reproduce the core predictions of my analysis in an experiment (see my description of it here), which would suggest that the assumptions are reasonably accurate (at least in my case).
What some get wrong
Ground loop noise from electromagnetic induction is not necessarily related to the current. Electromagnetic induction means that there are effectively parasitic voltage sources across the signal line, ground shield, and ground wiring. Even if no current is flowing, these will still create voltage differences.
In most circuits, increasing a resistance will increase the voltage drop across it, even though the current goes down (the simplest example is a voltage divider - this can be extended to other circuits using Thevenin's theorem). Changing the resistance of parts of the ground loop (e.g., by inserting \$10\Omega\$ resistor, or making its resistance \$\infty\$ by open circuiting the shield) will simply change how the noise voltages are distributed, but will not remove them.
Ground lifts with single-ended connections
Applying a ground lift to a cable shield is like taking the shield resistance to infinity. It causes all of the noise drop to occur across that gap - allowing the grounds on either end to float at completely different voltages, which will result in lots of noise added across the line. It will also prevent ground loop currents from flowing.
Whether this causes the noise seen at the receiver to improve overall depends on where most of the noise was coming from in the first place. If the noise was predominantly coming from the voltage across the shield, then it will make it worse. On the other hand, if the noise was primarily due to ground loop currents creating \$IR\$ drops within sensitive signal circuitry in the transmitter or receiver, then it will make it better. I suspect the former is more likely, since you can avoid the latter with good circuit design by ensuring that the signal ground is not placed in the path of ground loop currents (and it would tend to require larger trace resistances, high gain circuitry, or low signal levels). These parasitic \$IR\$ drops would also be problems for balanced lines.
However, even if internal \$IR\$ drops were the dominant factor, a ground lift could never completely reject the noise, since opening the ground shield puts the noise voltages directly in series with the signal (referring to the symbols in my question: \$V_s\$ would be directly in series with \$V_n\$ - so the ground lift will result in an SNR of \$V_s/V_n\$).
Ground lifts with other connections
If a signal cable is able to reject the ground noise across the line as a common-mode signal (e.g., balanced line fed into differential receiver), or if the noise can be tolerated for some other reason, then lifting the ground of a cable shield will improve things overall, since ground currents are stopped (preventing undesirable voltage drops elsewhere), while issues from noise voltages across the disconnected shield are avoided.
Current ratings
Another issue with induced ground currents is that it prevents loop currents from circulating through ground conductors that may not be rated for those currents (I don't know in practice how often ground currents can be that large and have only heard about it being a theoretical issue from other people).
Common-impedance coupling
People sometimes use the term "ground loop" to refer to issues where common-impedance coupling through mains ground conductors causes there to be undesirable voltage drops between the mains ground of two devices due to multiple devices pulling current through a shared ground resistance. This causes the devices to couple: current sunk by one device will by seen as a voltage shift in the ground of another device. This is a different phenomenon from what was discussed in the question.
In this case, the ground shield is in parallel with the rest of the ground wiring and helps to reduce the total resistance between the two grounds, resulting in a lower voltage drop (despite a slightly higher current). In this case, opening the ground shield will make this voltage drop larger and most likely worsen overall performance (unless, as before, parasitic drops within signal circuitry were more dominant). Ground currents from another device exceeding the rating of the ground shield is a possibility, but is a separate issue to noise.
Conclusion
Ground lifts have limited effectiveness when applied to the ground of single-ended lines, and will most likely make the noise worse. Even when they can improve the noise, they are limited in how effective they are. They make much more sense for balanced lines (in which case a ground lift on the receiver side is preferable to minimize filtering due to the line capacitance - as suggested by Handbook for Sound Engineers, 4th ed).
If the noise across the line is the dominant factor (and not internal \$IR\$ drops), then a ground lift will worsen the noise, and lowering the resistance of the ground shield will improve the noise. However, this is also of limited effectiveness in practice since it would be hard to get a cable with a shield resistance much below the mains wiring resistance (limiting noise attenuation to ~6 dB according to the formulas I derived in my question). It also has the disadvantage of increasing the loop current, increasing potentially problematic voltage drops elsewhere. To conclude:
Lifting the ground on one end of a single-ended cable will make the noise worse across that cable - it may prevent noise in other lines, and may actually improve the noise overall if parasitic \$IR\$ drops elsewhere were more dominant, but the full loop noise will still appear across that cable, which a single-ended cable cannot reject.
PersonWithName
  • 473
    IMO ground lift and other dodgy circuits used in audio by people not too familiar with emi are all terrible. this whole sector and its internet department is full of fairy tales and unreproducible voodoo advice. – tobalt Sep 12 '21 at 19:23
  • "how often induced ground currents are that large" if the two receptacles are in different buildings and/or earthed independently there can be a difference in potential and the shielding would become a fire or electrocution hazard due to equalizing currents or large static discharges. – P2000 Sep 14 '21 at 15:18
  • It's only a fire hazard if current ratings are exceeded. Most wires are rated to carry at least some amount of current. I'm just curious how often these currents are large enough to pose that risk in practice or if it's just a purely theoretical risk. It's a question of numbers. For static discharges - okay, but I'm not really sure why this necessarily has anything to do with ground loops as opposed to ground wiring or wiring in general. ESD is an electrostatic phenomenon that doesn't involve \$E\$ running in loops. – PersonWithName Sep 15 '21 at 00:40
CORRECT
"Professional audio equipment intended for use with balanced lines may have a ground lift switch for the cable shield." Ref Ground Lift
Example:
(Image source: Audio Science Review)
and
(Image source: Shure)
and
(Image source: ProSoundWeb)
The diagram in the other wikipedia page you reference, Common_ground_loops, is incorrect.
This is not a balanced line:
WRONG
(Image source: Wikipedia - Ground loop (electricity))
And as you analyzed and confirmed in experiments, it does not reduce induced noise. Perhaps this is your chance to make a useful and well-founded wikipedia edit.
Oddly, as you point out, the wrong diagram showing a break of the ground in a single-ended connection, is prevalent on the internet.
Lincoln said it best: "These days in America it is more difficult than in any other period in history to verify the truth of what a man reads on the internet" --- Abraham Lincoln
SamGibson
  • 17,231
  • 58
P2000
  • 3,087
    All - The long comment chain has exceeded what is reasonable for comments, and has become a discussion. Therefore it has been moved to chat and should be continued there (link below). -- As this bulk moving of comments to chat can only be done once, and new comments cannot be moved properly to chat later, *any further comments posted here might be deleted without notice*. **So keep it in chat from now onwards, please!** If any updates to the answer are decided during the chat, they can be made via an edit to the answer, as usual. Thanks. – SamGibson Sep 13 '21 at 05:02
  • Comments are not for extended discussion; this conversation has been [moved to chat](https://chat.stackexchange.com/rooms/129528/discussion-on-answer-by-p2000-why-does-analysis-indicate-that-ground-lifts-do-no). – SamGibson Sep 13 '21 at 05:03
The option of a ground lift exists mainly in connection with an audio transformer, typically in the context of a DI. Without a ground lift, the ground of the unbalanced signal source is connected with the ground of the (typically balanced) signal recipient. The ground loop current of any changing magnetic field, assuming near-zero resistance of the ground loop, will compensate any net magnetic field flow change through the loop while running through the devices themselves and inducing secondary voltages there.
When both instruments (like a keyboard and a mixer or amp) are already grounded, the potential of a balanced or unbalanced input cannot float to levels problematic for the input circuitry so one can safely separate the grounds.
An alternative for an amp with unbalanced input is a "poor man's ground lift" separating signal ground and earth via the AC inputs of a high voltage high current bridge rectifier that has the DC outputs short-circuited solidly so that it will withstand mains shortcircuit current long enough to trip a breaker.
Since the bridge rectifier will require at least 1.2V across to start conducting, it usually works as a ground lift while still preventing fatalities.
You can also introduce a "hum break" resistor (about 10Ohms, small enough to trigger a GFCI breaker that must be present) in the signal ground line to the first preamp stage. So that this actually helps in any way, the reference ground of the first input stage has to be on the side of the signal source rather than the amp. That way any input hum common to both signal and signal ground is not amplified by the first input stage. It is not eliminated either, but in comparison to the amplified signal after the first input stage it will be considerably less prevalent.
Most discrete or opAmp-implemented input stages are comparatively easy to modify in that manner.
Those approximations of a ground lift for unbalanced signals can help making an amp or similar more robust against ground loop hum. An actually balanced signal/connection in combination with an explicit ground lift separating redundant (non-signal) ground connections will be preferable.
A ground lift only makes sense when the arriving signal is balanced (trivially when generated with a transformer, but possible also by routing both signal and return signal voltages through equal resistors, even when the return signal voltage is not actually the inverted main signal but just signal ground) and the differential between signal and return is what is getting amplified.
In that case it breaks the ground loop while not affecting the differential between signal and signal return.
  • Can you elaborate on the "hum break" resistor? And what does it have to do with GFCI? Perhaps a quick sketch could help. I am not following where that resistors sits and how it might help deal with "input hum". – P2000 Sep 13 '21 at 00:45
It is an undeniable fact known to many users of audio equipment that mains frequency hum or buzz may appear in a sound system at the moment a ground loop is created, and may disappear at the moment that ground loop is broken.
The effect may occur with either balanced or unbalanced connections.
The question above describes a model in which hum or buzz is NOT ameliorated by breaking a ground loop. Such a model is helpful in understanding why grounding a cable shield on one side only sometimes doesn't improve matters, but fails to explain why ground lifts sometimes work.
Ground lifts can ameliorate mains frequency hum or buzz when the equipment to which the shielded cable is connected is, either through oversight, or through faulty reasoning, or even intentionally, not designed to properly handle ground current.
The designer may have assumed that it is the end user's responsibility to avoid or break ground loops. Or the a designer may not have understood the consequences of his or her design choices with respect to ground loop induced noise. But, for whatever reason the equipment
  1. Has a nontrivial impedance between the cable shield and the protective mains ground, and
  2. The voltage developed across that impedance by ground loop current is coupled to the circuit and amplified along with the desired signal.
Equipment may be tested for such conditions by applying a mains frequency (but not mains voltage!) current between the cable shield connector to the safety ground connector. If this creates a hum or buzz in the output, there is nontrivial impedance between those points, and some of the voltage developed across that impedance is coupled with the signal and amplified.
A "quick fix" solution to hum and buzz in such equipment is to break the ground loop with a ground lift switch. Alternatively, the ground loop may be broken by using an transformer, or other galvanic isolation technique. But perhaps the best solution is to fix the equipment by soldering a wire with sufficiently low resistance from the connector's shield pin directly to the safety ground connection within the equipment, bypassing any amplification circuitry.
Note that modern PCB design practices, such as the use of ground planes, will tend to prevent such situations in the first place.
Edit: I am adding an example of model of a system with an unbalanced signal and with a ground loop, which benefits from a ground-lift.
The following shows the behavior of the circuit. enter image description here
The first part of output is with the ground lift switch open, and the second part with the ground lift switch closed. As can be seen, the ground lift switch benefits the signal to noise ratio quite a bit. The model doesn't include the wire resistances in the signal line, or in the ground loop (except between the potentiometer "ground" and the amplifier "ground". As a result, the ground loop current is not realistic. This is done to make the issue apparent in a graph of the output signal. A signal to noise ratio of, say, 40 dB, will be noticeable to the ear. However, it would be hardly noticeable in a linear-scale graph of the combined signal and noise with time.
The model can be corrected to include resistance in the cable shield, and also resistance in the mains ground wire. This resistance can significantly improve the S/N ratio. Similarly, a ground lift resistor between the cable shield and the potentiometer "ground" will also improve S/N ratio.
Although making the model more realistic will (usually) improve the S/N ratio, the principle remains.. Ground current within this particular receiving equipment negatively affects the signal to noise ratio, and breaking the ground loop with a ground lift switch which disconnects the cable shield, or adding a resistor in series with the cable shield, improves the S/N ratio.
Math Keeps Me Busy
  • 18,947
  • 65
  • I agree that ground lifts sometimes reduce noise, and my analysis (read my updated answer) explains it. I disagree that it reduces noise when used for unbalanced cables though. "It is an undeniable fact known to many users of audio equipment ... balanced or unbalanced connections" - I think these people are wrong. Most are not electrical engineers and even those who are I suspect haven't thought too much about it and take what the internet says for granted. They probably found that they work on a balanced cable or the mains ground (safety aside) and extrapolated that to unbalanced cables. – PersonWithName Sep 17 '21 at 12:21
  • If you break the cable shield, you expose the receiver to the full noise voltage as shown in my analysis and verified by my experiment. This voltage does *not* come from an IR drop, but from Faraday's law. – PersonWithName Sep 17 '21 at 12:21
  • "Has a nontrivial impedance between the cable shield ..." If this impedance you're referring to is directly in series with the cable shield then I completely agree and this is what my analysis shows. Higher impedance of cable shield = worse. A ground lift on a signal cable shield makes this impedance infinite. "The voltage developed across that impedance ... is coupled to the circuit and amplified ..." You're going to need a diagram here to illustrate what impedances and voltages you're talking about. – PersonWithName Sep 17 '21 at 12:22
  • Current flow is bad if the current ratings of ground wires are exceeded and the wire burns up. However, I have not seen any evidence of a ground loop generating large enough currents causing this to happen and I suspect it is rare at the very least. However, as far as noise seen by the receiver goes, voltage is the problem. For most circuits (except some more exotic exceptions), if you increase a resistance, you will *increase* the voltage drop across it, *even though the current decreases*. E.g., consider a voltage divider. You can generalize this to more complicated circuits. – PersonWithName Sep 17 '21 at 12:22
  • Note that I completely agree that having high impedances in ground wiring can cause problems due to IR drops. This is called common-impedance coupling. Some people refer to these as ground loops too, but it is actually a completely separate phenomenon to "inductive" ground loops that I have been discussing. However, even in these cases, you do not make things better by open circuiting a ground shield - this just increases the impedance between two ground points... *Just because current can no longer flow across an open circuited ground shield, doesn't mean there is no voltage drop across it* – PersonWithName Sep 17 '21 at 12:22
  • In fact, a ground lift could even work in an unbalanced cable by preventing ground loop noise in other cables that form the loop. The only issue would be that the unbalanced cable with the ground lift would have absorbed all of that noise for itself. If that noise is not a problem somehow (e.g., maybe less of a problem for digital signals...), then I guess the ground lift "works" in that case, but only because it redistributed the noise to somewhere where it isn't as much of a problem, not because it removed the noise (the induced electric fields are still circulating around the loop!) – PersonWithName Sep 17 '21 at 12:33
  • I have added an example where a circuit receiving a single ended signal benefits from a ground lift. It would benefit from a higher shield resistance as well. Or a ground lift resistor between shield and receiver ground. The values are somewhat exaggerated to make the point graphically visible. Unfortunately, a buzz in a signal with a S/N ratio of 40dB is quite noticeable to the ear, but is not visibly noticeable in a linear signal graph. Reduce the ground loop current, to more realistic levels and you won't _see_ the buzz, but you will hear it. – Math Keeps Me Busy Sep 26 '21 at 03:50
  • The output voltage you're measuring in that simulation is not the voltage that the receiver would be reading (which would be the branch voltage across the 10k pot scaled down by the potentiometer setting). Instead, you're measuring the node voltage with respect to some other point on the circuit that you've designated as ground. To correctly measure the receiver voltage, the ground symbol should be placed at the base of the 10k pot so that the node voltage equals the branch voltage that we want to measure. – PersonWithName Sep 27 '21 at 07:22
  • @hddh I think you are missing the point. The point is that ground loop current is causing noise in the receiver and the ground lift ameliorates that noise. Thus, your conclusion that ground lift switches don't work is in error. They don't work in some cases, but work in others, depending upon the equipment involved. – Math Keeps Me Busy Sep 27 '21 at 11:13
  • In your example, the closed ground lift switch is not causing noise in the receiver. It's causing noise in some random node voltage that has no physical significance since the noise voltage and ground wire resistance will actually be distributed elements, so the ground reference in the posted example doesn't correspond to anything physically meaningful. Your circuit produces the opposite result if you measure the receiver branch voltage. Besides, if you read my answer (which I have been updating recently) I never make that conclusion anyway. – PersonWithName Sep 27 '21 at 13:20
  • The title of your Q is "why does analysis indicate that ground lifts do not fix ground loops". You stated that you "disagree that it reduces noise when used for unbalanced cables though." And you claim that "the ground reference in the posted example doesn't correspond to anything physically meaningful." But someone listening to the output of that equipment will definitely notice the difference in S/N ratios between ground lift switch open and closed. The ground in the circuit is the reference to which the op-amp output is paired. Not sure you are getting it. – Math Keeps Me Busy Sep 27 '21 at 13:44
  • I was not clear on what your 10mOhm resistance represented - and it matters. Sure you can construct some arbitrary circuit, but if it doesn't correspond to a ground loop scenario you are likely to encounter in real life, it doesn't really show anything. If your 10mOhm resistance is supposed to refer to the parasitic resistance of the ground wiring, then the voltage you are reading has no physical relevance. An op-amp in the receiver could never be referenced to that point. – PersonWithName Sep 30 '21 at 09:48
  • If your 10mOhm resistance represents some parasitic trace resistance *inside* the device, then okay, that is a valid point. I had already discussed this somewhat in my answer under the section "Other issues due to current". So yes, it's technically possible for opening a ground lift switch to improve the SNR. A few points on that: – PersonWithName Sep 30 '21 at 09:48
  • (a) The actual resistances that would be present in practice mean you're unlikely to get much benefit from opening the shield. In your case, the parasitic trace resistance consists of 100% of the impedance around the ground loop, which is very unrealistic. If you start adding in other resistances around the loop it becomes much less effective. Even a 50mOhm ground shield and 50mOhm ground wiring means don't get much benefit at K=0.05. At K=1, it gets worse when you open it (so the switch would have to be flipped when you change volumes to get the optimal SNR!). – PersonWithName Sep 30 '21 at 09:49
  • (b) Opening the ground switch can never improve the SNR beyond Vs/Vn (since the noise is fully in series with the signal). So even if the numbers are just right to make it improve the SNR, it's not really the best solution. The change in SNR in your example was very dramatic because the pot was set so low. Even at half volume you barely get any benefit. At full volume with just 50mOhm ground wiring and 50mOhm shield (i.e., trace is 9% of the total ground loop resistance), it gets worse when you open it. – PersonWithName Sep 30 '21 at 09:51
  • I'm not even saying that having the ground shield connected is better. In my answer I said that "lower impedance shield was better", but in practice it would be hard to get the shield impedance much below the ground wiring impedance, limiting the attenuation of noise to around 6dB (and this matches my experiment too). So the conclusion really is that raw single-ended cables just aren't very good for this. Ground lifts on them might improve the SNR, but they're probably make it worse, and even when they work, they have limited effectiveness. Other solutions are better. – PersonWithName Sep 30 '21 at 09:54
  • If I have time, I'll update my answer to make these things more explicit. I might reword my conclusion a bit. – PersonWithName Sep 30 '21 at 09:55
  • And due to the ground loop inductance, even when opening the switch improves the SNR at lower frequencies, there will be a transition point at a higher frequency after which the SNR is worsened by opening the switch. However, I don't know if the inductance of the ground loop is large enough for this transition point to be in the audible range. – PersonWithName Sep 30 '21 at 10:02