Using GFCIs with transformer or other high-inrush current loads is problematic, because in some designs the differential transformer core can locally saturate and produce an invalid output in the sense winding, tripping the GFCI - without any ground leakage.
What are the standards/requirements applying to GFCIs (in various markets) in terms of maximum peak current they must handle without spurious tripping? I'd expect this peak rating to be higher than continuous rating.
Most GFCIs on the market do not specify such current in their spec sheets/datasheets, thus I presume that the actual requirement would be buried in a standard somewhere...
This question is about applications where a load may present, say, 10Arms continuous current, but have 10x+ higher inrush current (e.g. 100A or more). In practice, I've seen many GFCIs rated at 2x the continuous current (20A in this example) trip spuriously at 100A half-wave inrush. I would be surprised if this requirement wasn't addressed in the standardese, thus the question.