My apartment is supplied with 2 sources of electricity: the grid and a generator in the apartments premises. The change over is controlled by an ACCL. The apartment has an 25A ELCB/RCCB with 100mA sensitivity. The power to individual rooms is further protected by an MCB for each room.
When the generator is switched off, the RCD in the apartment trips. This does not happen when the grid fails, but happens every single time when the generator is switched off. The generator supplies electricity to some 200 other houses, and the RCD tripping issue occurs only at my apartment.
Tests I have done so far:
- Switched off the MCB for individual rooms one at time. I was trying to isolate if any specific MCB/room has a fault. The RCD failed every time.
- Switched off all unnecessary devices when running on generator. Every single device was turned off excluding my internet modem and wifi router. The RCD failed this time too.
- Used a multi-meter to check the voltage difference between neutral and earth. It is 0V when running on grid. It was 9V when running on generator. But when I tried to reproduce this for the apartment's maintenance manager, it turned out to be 0V.
- Replaced the ACCL and the RCD with new devices of same specification as earlier. The issue persists.
The maintenance manager recommends changing the RCD to a 300mA sensitivity. But I am not convinced without proving the source of the issue. What can cause such tripping? Are there any other tests I can conduct with simple instruments at home (multi-meter)?