1

I have a DC-DC converter (24v to 12v) that has terminal block at its input and output terminal. To understand it better, I've attached the drawing of the converter found in its datasheet. DC-DC Converter drawing

Problem: This converter is used at work. And the existing configuration connected by others has multiple wires with fork connector end connected to each of the screw at output terminal.

enter image description here

Question is: Is it safe to be stuffing multiple wires with fork connector end into one screw terminal? And what is the understanding behind?

If further clarification is needed, feel free to leave a comment. Thanks for your interest and help.

Shuan
  • 13
  • 3

3 Answers3

2

From the comment to @Mattman944's answer it appears that your question is based on a poor understanding of how voltage and current interact.

Actually my main concern is whether the 2 fork connectors (as in pic above) would result in a short circuit scenario when they are in contact with each other.

In effect you really want a short circuit. Both wires should have the minimum resistance to the terminals and since they are in close contact and screw clamped together the resistance between each other and the PSU terminal will be very low as in a "short-circuit".

schematic

simulate this circuit – Schematic created using CircuitLab

Figure 1. (a) A good circuit. When the switch is closed LAMP1 will light. (b) A short-circuit. When SW2 is closed a high current will bypass LAMP2 via R1. Hopefully F2 will blow.

The term short-circuit is usually used in the context of an unintended alternate route between two points in a circuit.

The resistance of the 2 wires are different. And the 2 wires draw different amount of current.

The wires will be sized according to their load.

Could there be a case where current drawn to fork connector 1 flows into fork connector 2, and thus resulting in excess current into wire with fork connector 2 (because the fork connectors are in contact)?

schematic

simulate this circuit

Figure 2. The current drawn by LOAD1 does not affect the current drawn by LOAD2.

No. Current flows in a loop. The current that flows into fork connector 1 is used by the load on that circuit. It can't induce additional current in the other circuit. (Note that one load can cause the voltage to sag a little and that will affect all the other loads connected to the power supply. You may have observed your house lights dim when a large load is switched on.)

Is it safe to be stuffing multiple wires with fork connector end into one screw terminal? And what is the understanding behind?

Yes, provided adequate contact is made and the terminal is rated for the combined current.

Electrically the situation is the same as you plugging in various items into your household supply. With a constant voltage supply each load draws the current it requires without affection the others.


From the comments:

: 1. When converter is on, we know the screw of at the terminal is at output voltage (this case, 12v).

OK. But 'V' for volt. (The symbol is uppercase. The spelled out word is lower as for all SI units named after a person.)

  1. Assume the case where 2 forks are not in contact with each other initially (because of the plastic protruding insulations just above the lugs as seen in the above pic, they prevent the screw to be screwed all the way in to keep the forks together).

That's not the situation. Look what the guys in forensics found after image enhancement:

enter image description here

Figure 3. The fork terminals have been correctly installed back to back to ensure full contact of the forks without straining due to interference of the crimp barrels. Fork (1) is installed "upside down" and fork (2) is installed "right-way-up".

enter image description here

Figure 4. Fork terminals are not symmetrical about the horizontal plane through the barrel centre. When installing two into one terminal it is advisable to mount them back to back.

And assume the forks are in contact with the screw in the terminal, so current will be drawn by each of the fork to their wires.

The whole terminal, fork, fork, screw arrangement is now one conducting mass of metal. All points should be at the same potential.

  1. Now, say because an accidental nudge to one of the wires (while the circuit is running), and then the 2 forks which are already carrying their respective current come in contact. Could this induce a short circuit?

No. If installed properly they are fully in contact already.

Could this be similar to how 2 live wires touch each other and cause a spark?

No. Two live wires1 touching each other won't cause a spark because they're both live and at the same voltage. You'll only get a spark when two wires of different voltages touch each other.

1Assuming that they're on the same phase of the supply.

Transistor
  • 168,990
  • 12
  • 186
  • 385
  • Thank you for your elaborate reply. Appreciate your effort. Understand your explanations: 1. On short circuit. 2. Current through wires depends on what the load needs. 3. Current need of a load does not affect the current need of another load, thus their respective wires carry only the needed amount of current. – Shuan Mar 19 '20 at 13:08
  • To elaborate further on the scenario i thought might happen: 1. When converter is on, we know the screw of at the terminal is at output voltage (this case, 12v). 2. Assume the case where 2 forks are not in contact with each other initially (because of the plastic protruding insulations just above the lugs as seen in the above pic, they prevent the screw to be screwed all the way in to keep the forks together) And assume the forks are in contact with the screw in the terminal, so current will be drawn by each of the fork to their wires. – Shuan Mar 19 '20 at 13:09
  • 3. Now, say because an accidental nudge to one of the wires (while the circuit is running), and then the 2 forks which are already carrying their respective current come in contact. Could this induce a short circuit? Could this be similar to how 2 live wires touch each other and cause a spark? – Shuan Mar 19 '20 at 13:10
  • Sorry for the multiple posts due to word limit, and the poor formatting. Thanks again for your time and effort. Appreciate it. – Shuan Mar 19 '20 at 13:13
  • See the update. – Transistor Mar 19 '20 at 13:33
  • Thanks again for your effort. Doubt is cleared. Cheers – Shuan Mar 19 '20 at 14:04
1

I have seen this done many times, it is generally OK.

What is important, is that the screw is fully engaged into the receiving threads. For many terminal blocks that I have used, the threads are mashed (if there is a technical term, I don't know it) on the other side to make the screw weakly captive. When you loosen the screw, you should never force it into the mashed portion. The resistance will increase when this happens, stop, don't loosen any more.

If you can get the fork (spade) into the block without going into the captive threads, it should be OK. If you force it into the captive threads, you will weaken it and likely strip the threads when you tighten. I know, I have done this a few times before I learned better.

Mattman944
  • 13,638
  • 1
  • 19
  • 43
  • Thank you for the reply. Actually my main concern is whether the 2 fork connectors (as in pic above) would result in a short circuit scenario when they are in contact with each other. The resistance of the 2 wires are different. And the 2 wires draw different amount of current. Could there be a case where current drawn to fork connector 1 flows into fork connector 2, and thus resulting in excess current into wire with fork connector 2 (because the fork connectors are in contact)? Once again, thanks for your answer above. – Shuan Mar 19 '20 at 10:34
  • @Shuan unless one of the devices the wires are connected to actually source current you're good to go in that aspect. The converter will deliver the right voltage provided the two appliances don't draw too much current. For the current itself it will be split among the two wires based on each device needs. A wire with more resistance will just get hotter but it will depend on the amount of current required by your application. This is not a short circuit scenario (unless you connect the 0V wire to the 12v output) – zakkos Mar 19 '20 at 10:40
  • @zakkos Thank you for your reply. Understand your points. – Shuan Mar 19 '20 at 13:10
1

I have done that many times. However, I am not at all confident that it is a good practice. I would say that it would be bad to have more than two connectors on a terminal. When two terminals are connected, it would be better to use ring lugs than spade lugs. Of course that can only be done if the screws are not captive (or weakly captive). I would recommend inverting the lug next to the block so that the ferrules don't force the lugs apart.

The issues are all about the mechanical connection. The only time you need to worry about current division is when the wires are completely parallel, connected to the same point on each end. You do need to be concerned about the total current. Terminals have maximum current ratings just as wires do.

  • Thank you for suggestions. Will consider the use of ring lugs, as I suppose they're less likely to come off than spade lugs. – Shuan Mar 19 '20 at 12:27
  • Ring lugs will be less likely to shift when tightened. When inserting two forked lugs, it is easy for the bottom one to slip out a bit and end up with less contact surface. Also, with forks, contact surface is less to begin with. –  Mar 19 '20 at 14:20