5

The transformer rating is given in kVA, but the load connected is always considered in watts. Why?

Eventhough, the load active power is represented in watts it has some reactive power, right?

Is the total power consumed by load (active + reactive) equal to the power supplied by the secondary side (secondary voltage × seconadary current) which is apparent?

winny
  • 13,064
  • 6
  • 46
  • 63
akhil
  • 51
  • 3

4 Answers4

4

"Watts" of a load signifies the Real/Active power. It is the useful power consumed by it. Reactive power is not useful. Consumers are normally charged by the utilities only for the real power.

$$P_{real} = P_{app} cos \phi $$
\$ \cos \phi \$ is the power factor of the load,

While KVA of transformer signifies its rated apparent power. It defines the maximum current you can draw from the primary/secondary for given voltage. Above which, copper losses cause windings to heat up.

Marcus Müller
  • 88,280
  • 5
  • 131
  • 237
Mitu Raj
  • 10,843
  • 6
  • 23
  • 46
  • 1
    And why should core losses be affected by load current? I trust you don't think saturation is caused by secondary currents? – Andy aka Mar 21 '18 at 17:06
  • Yea thats right. So its Just copper losses . – Mitu Raj Mar 21 '18 at 17:14
  • @Andy Strange, I have seasoned fellow EEs at work who does the same assumption as both Mr Raj and Tony. Something wasn’t taught in school around the world it seems. – winny Mar 21 '18 at 17:26
  • @winny Actually In my country, They have separated Electrical and Electronics into two different fields of study. I am graduated from Electronics. We were hardly taught about transformers, power transmission stuffs and all. Ha could be the root of my "assumption" lol. – Mitu Raj Mar 21 '18 at 17:34
  • @winny don't worry , sometimes I make misteaks – Tony Stewart EE75 Mar 21 '18 at 18:28
4

The transformer rating is given in kVA, but the load connected is always considered in watts. Why?

If the load on the secondary is purely reactive then using "watts" does not account for this type of load. However, "VA" accounts for any type of load on the secondary from capacitive through purely resistive to inductive.

Andy aka
  • 434,556
  • 28
  • 351
  • 777
3

major re-write

In a transformer, losses are of two types

  • Constant losses or core losses - These depend on V
  • Variable losses or ohmic (I2R) losses - These depend on I

Hence total losses depend on V and I.

  • Since rating of transformer depends upon losses,
    and losses depends upon V and I,
    hence the rating of transformer depends upon V×I,
    which is also termed as VI rating, in units of VA, kVA, MVA.

  • As losses are independent of the power factor of load,
    the rating of the transformer is also independent of load and can be only decided based on losses.

    That’s why transformer is generally specified with apparent power rating (VA or KVA) and not in KW

Tony Stewart EE75
  • 1
  • 3
  • 54
  • 182
  • 1
    Why would it take more peak magnetic flux to provide more VAr? Primary side exited the core with very constant volt-second area and your VAr only takes up available current headroom in your windings and power lines. – winny Mar 21 '18 at 16:26
  • 1
    Secondary load current does not affect saturation of the core. How old are you @Tony LOL? – Andy aka Mar 21 '18 at 17:04
  • 1
    Too old, I’d rather be golfing – Tony Stewart EE75 Mar 21 '18 at 17:19
  • Even after your edit, eddy currents in the conductors increase, but the frequency is too low for this to matter. Magnetic losses stay virtually unchanged in the transformer with increased load just like dielectric losses. What you end up with is “just” increased resistive losses. – winny Mar 21 '18 at 17:24
  • @Winny as you know , the difference between VA supply rating and W load rating is due to network losses: {mainly Electric( conduction, skin effects) and Magnetic: core(hyst&eddy) not necessarily related to customer W load – Tony Stewart EE75 Mar 21 '18 at 18:07
  • Yes, but your assumption is still that transformer hysteresis losses or saturation has anything to do with load, active or reactive. – winny Mar 21 '18 at 18:27
  • No My assumption is that the VA input rating includes these which has nothing to do with the output rating. – Tony Stewart EE75 Mar 21 '18 at 18:29
2

Actually, if the load is highly reactive and near the rating of the transformer, then ignoring the reactive component can be dangerous. Technically, the transformer load should be evaluated in VA rather than watts.

If, in an industrial environment, those designing the setup are actually ignoring the VA of large reactive loads when specifying a transformer then they should have their sliderules, er, calculators, er, smartphones taken away from them.