72

According to this article (and a lot more published today on the same topic), Kosovo electricity net production balance has decreased during the last weeks.
This has led to a small deviation of the European network’s frequency (from 50Hz to 49.996Hz). In turn, this frequency deviation led to some electric clocks (like ones in ovens) being out of sync (up to 6 min since January).

  • How can a decrease in electricity production lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?
  • If the loss of power from some countries causes a frequency deviation, shouldn't we also observe other impacts, like a drop of the output voltage? Does this mean that we've also been experiencing a drop of voltage for weeks here in Europe?
  • Why do some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology? This means the same oven needs two different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.
Evariste
  • 733
  • 1
  • 5
  • 11
  • 51
    The kind of oven clock that gets timing from the grid probably doesn't have any firmware. – The Photon Mar 07 '18 at 17:56
  • 2
    See also https://electronics.stackexchange.com/questions/360258/why-do-generators-have-to-rotate-at-a-slower-frequency-if-demand-outpaces-the-su –  Mar 07 '18 at 18:01
  • 10
    Possible duplicate of [Why do generators have to rotate at a slower frequency if demand outpaces the supply?](https://electronics.stackexchange.com/questions/360258/why-do-generators-have-to-rotate-at-a-slower-frequency-if-demand-outpaces-the-su) – Andy aka Mar 07 '18 at 18:03
  • To answer your 2 last points: yes you will experience voltage drop. Some power transformers include an automatic system to adjust output voltage in steps of maybe 0.5% or so. When voltage increases/decreases too much, the setting changes until reaching minimum/maximum setting. Most power grids allows for variations of ±5% around nominal. Some (legacy) oven may not use quartz crystals because it is cheaper to simply rely on approximately 50/60Hz frequency. It is not like if you were expecting atomic clock accuracy from your oven clock, don't you? – Mishyoshi Mar 07 '18 at 18:08
  • 6
    @Andyaka hmm.. actually that does not really answer the question over the long time. The real question here is, why didn't the system recover running at 50.111 long enough to catch up. – Trevor_G Mar 07 '18 at 18:09
  • @Trevor_G Why would the system run on 50.111Hz and who said it won't recover? – Eugene Sh. Mar 07 '18 at 18:18
  • 8
    @EugeneSh many grids try to keep the pulses per day constant catching up during off-peak periods. – Trevor_G Mar 07 '18 at 18:19
  • @Trevor_G I see. Didn't know this. Are they actually worrying about these systems relying on the frequency to synchronize? Apparently not the Kosovo system :) – Eugene Sh. Mar 07 '18 at 18:21
  • @EugeneSh It has not recovered in weeks, how that could be? I expect a short frequency drop when a power plant fails, quickly followed by a short frequency increase when a backup plan takes over. Why this has not happened in this case? Political or technical reasons? – Evariste Mar 07 '18 at 18:21
  • 2
    @Evariste whomever runs the grid in your area of the world apparently does not care about the daily average or has poor control over it. – Trevor_G Mar 07 '18 at 18:23
  • 2
    @Trevor_G maybe... but we talk about a large part or Europe here, including Switzerland! :) – Evariste Mar 07 '18 at 18:25
  • 3
    Yup.. that's why I said that is the real question... Why it slows down is explained and understandable... why they did not recover is another issue entirely and probably has more to do with people than wiring. – Trevor_G Mar 07 '18 at 18:26
  • 3
    Also - why haven't generators in other countries increased their output to compensate? – user253751 Mar 07 '18 at 21:51
  • 10
    Back in my student days, I got an alarm clock for free : the downside was that it was designed to get its timing from a 60Hz grid, and I used it in Europe. It got 4h late every day, and was an interesting arithmetic problem to solve before going to bed every night : "What time should I set the alarm to if I want to wake up at 07:30?" – Eric Duminil Mar 08 '18 at 07:42
  • Not only is @ThePhoton right, but there's a correlation between ~120V 60Hz and ~230V 50Hz. An oven would be built differently for the two voltages anyway. The exceptions can be treated as edge cases (from [wikipedia](https://en.wikipedia.org/wiki/Mains_electricity_by_country#Voltages) with a little tidying: 110V,50Hz:Barbados, Bolivia, Curaçao, Libya, Madagascar, Morocco. 230V,60 Hz:Peru, Saint Martin (French), Saudi Arabia, South Korea, Antigua and Barbuda, Philippines) – Chris H Mar 08 '18 at 10:10
  • 1
    Am I the only one who was trying to figure out what "row delays" were? – Michael Mar 09 '18 at 16:46
  • @Michael it is like row hammer, but affects clocks instead. –  Mar 09 '18 at 19:11
  • 3
    This is a capitalist scheme to steal hours from the workers. The clock will speed up at night when the workers are at home. – richard1941 Mar 09 '18 at 22:00
  • @EricDuminil wait - your clock would get behind by four *hours* every day? Or at least get so delayed it practically wasn't a clock. ...I wonder how that even made it to market (...granted you got it free so maybe that was the only way they could sell them) – BruceWayne Mar 10 '18 at 19:02
  • 5
    @BruceWayne: The clock was brought to Spain by my roommate from the US. He didn't realize it wouldn't work well with the local grid, and gave it to me. – Eric Duminil Mar 10 '18 at 19:08

5 Answers5

50

From the Reuter's article referenced:

SARAJEVO, March 7 (Reuters) - European power grid lobby ENTSO-E urged Serbia and Kosovo to urgently resolve a dispute over their power grid, which has affected the broader European network, causing some digital clocks on the continent to lose time.

enter image description here

Figure 1. The ENTSO-E System Operations Committee has 5 permanent regional groups based on the synchronous areas (Continental Europe, Nordic, Baltic, Great Britain, and Ireland-Northern Ireland), and 2 voluntary Regional Groups (Northern Europe and Isolated Systems). Source: ENTSO-E.

The European grid shares power across borders. AC grids have to be kept 100% in-sync if AC connections are used. Britain and Ireland, for example, are connected to the European grid by DC interconnectors so each nations grid can run asynchronously with the rest of Europe whilst sharing power.

The grid shared by Serbia and its former province Kosovo is connected to Europe’s synchronized high voltage power network.

As explained above.

ENTSO-E, which represents European electricity transmission operators, said the continental network had lost 113 gigawatt-hours (GWh) of energy since mid-January because Kosovo had been using more electricity than it generates. Serbia, which is responsible for balancing Kosovo’s grid, had failed to do so, ENTSO-E said.

The energy hasn't been lost. It was never produced.

According to NetzFrequenzMessung.de (you might want to translate) the 113 GWh shortfall averages out to about 80 MW continuous on a total of 60 GW capacity. That's a 0.13%. The scary thing is that we're actually maxed out and can't find an extra 0.13%!

The loss [sic] of energy had meant that electric clocks that are steered by the frequency of the power system, rather than by a quartz crystal, to lag nearly six minutes behind, ENTSO-E said.

"Steered" is probably a mistranslation. "Regulated" would be better.

Many digital clocks, such as those in alarm clocks and in ovens or microwaves, use the frequency of the power grid to keep time. The problem emerges when the frequency drops over a sustained period of time.

enter image description here

Figure 2. An electro-mechanical timeswitch of the style popular with the utility companies.

Analogue, motorised clocks do too. The day / night clock on my electricity meter is > 40 years old and it has a mains-powered clock with a self-rewinding clockwork UPS to keep it OK during power cuts!

ENTSO-E said the European network’s frequency had deviated from its standard of 50 Hertz (Hz) to 49.996 Hz since mid-January, resulting in 113 gigawatt-hours (GWh) [sic] of lost energy, although it had appeared to be returning to normal on Tuesday.

The frequency is not held constant to three decimal places for months on end. That might be an average figure. Here's the data for the last five minutes:

enter image description here

Figure 3. Note that frequency deviation will be much wider over a longer time period. Source: MainsFrequency.com.

enter image description here

Figure 4. Network time deviation has increased from -100 s to -350 s in three weeks. Source: MainsFrequency.com.

enter image description here

Figure 5. [WOW!] In our previous measurement operation (July 2011 to 2017), network time deviations of ± 160 seconds occurred (June 2013). But since January 3, 2018, the network time deviation is continuously decreasing. Changing the setpoint for the secondary control power on January 15 from 50,000 Hz to 50,010 Hz has not yet been able to reduce the mains time. Source: MainsFrequency.com.

Secondary control power is activated when the system is affected for longer than 30 seconds or it is assumed that the system will be affected for a period longer than 30 seconds. Prior to this, deviations in the system are only covered through primary control. Source: APG.at.

“Deviation stopped yesterday after Kosovo took some steps but it will take some time to get the system back to normal,” ENTSO-E spokeswoman Susanne Nies told Reuters. She said the risk could remain if there is no political solution to the problem.

If they start generating and feeding into the grid it will speed up.

The political dispute centres mainly on regulatory issues and a row between Serbia and Kosovo over grid operation. It is further complicated by the fact that Belgrade still does not recognise Kosovo.

“We will try to fix the technicalities by the end of this week but the question of who will compensate for this loss has to be answered,” Nies said.

This doesn't make any sense to me. Energy flow is metered and billed accordingly. Each country pays for their imports.

ENTSO-E urged European governments and policymakers to take swift action and exert pressure on Kosovo and Serbia to resolve the issue, which is also hampering integration of the western Balkans energy market required by the European Union.

“These actions need to address the political side of this issue,” ENTSO-E said in a statement. The grid operators in Serbia and Kosovo were not immediately available to comment.

Kosovo seceded from Serbia in 2008. Both states want to join the European Union but Brussels says they must normalize relations to forge closer ties with the bloc.

Serbia and Kosovo signed an agreement on operating their power grid in 2015. However, it has not been implemented yet as they cannot agree on power distribution in Kosovo amid conflicting claims about ownership of the grid, built when they were both part of Yugoslavia. (Writing by Maja Zuvela; Editing by Susan Fenton)

I guess neither of the above are electrical engineers.



Answering the questions:

  1. How a decrease in electricity production can lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?

If demand is approaching peak capacity then we have to let either the voltage or the frequency droop if we wish to avoid disconnecting customers. Dropping the voltage will cause problems with certain loads and is to be avoided.

The Reuter's article fails to explain why the system average frequency has been low for so long. It can only be that it hasn't been able to run above 50 Hz for long enough to catch up. Off-peak seems the time to do this but there will be an upper limit on the frequency deviation - about 50.5 Hz (but I don't have a definite number).

  1. If the loss of power from some countries causes a frequency deviation, shouldn't we also observe other impacts, like a drop of the output voltage? This means we've also been experiencing a drop of voltage for weeks here in Europe?

No, we reduce frequency to avoid the drop in voltage.

  1. Why some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology?

They don't sync the clocks in the sense of adjusting or correcting the time. They maintain synchronisation by keeping the average frequency at exactly 50 Hz. One reason for this is the millions of electro-mechanical clocks in service. These are fantastically reliable, don't require batteries and do the job. Why replace them?

This means the same oven needs 2 different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.

Crystals will drift and the further complication of real-time clock with battery backup are required. Electrical utilities work on timescales of 20 to 50 years. How long do you think the electrolytic capacitors in your digital clock will last?


Links:


Other interesting bits:

This grid time deviation is constantly balanced out. If the time deviation is more than twenty seconds the frequency is corrected in the grid. In order to balance out the time deviation again the otherwise customary frequency of 50 Hz (Europe) is changed as follows:

49.990 Hz, if the grid time is running ahead of UTC time

50.010 Hz, if the grid time is lagging behind UTC time

Source: SwissGrid.

Meanwhile on 2018-03-08:

NTSO-E has now confirmed with the Serbian and Kosovar TSOs, respectively EMS and KOSTT, that the deviations which affected the average frequency in the synchronous area of Continental Europe have ceased.

This is a first step in the resolution of the issue. The second step is now to develop a plan for returning the missing energy to the system and putting the situation back to normal.

Source: ENTSO-E.

Hmmm! They're referring to it as "missing energy".

Transistor
  • 168,990
  • 12
  • 186
  • 385
  • 6
    "mainsfrequency.com"? Seriously? I'm amazed of what can be found on the internet. +1 for this. – dim Mar 07 '18 at 20:06
  • Still does not explain why time error correction did not correct it. – Trevor_G Mar 07 '18 at 22:26
  • 15
    We're pedaling as hard as we can over here to get the frequency up above 50 Hz for long enough to resync the clocks. We need those eastern guys to stop quarreling and get back on their bikes. OK I'll see if I can answer the actual questions but it's bedtime. ;^) – Transistor Mar 07 '18 at 22:32
  • LOL ha... back on yer bike then.. ;) – Trevor_G Mar 07 '18 at 22:36
  • 2
    Right, @Trevor_G: More pretty pictures for you. I'm having to look all this stuff up as I don't work in the power industry. It's rather interesting but if I'm tired in work tomorrow it's your fault. – Transistor Mar 07 '18 at 23:20
  • 3
    Is it because they can't find 80 MW of generation, or are there other constraints they're trying to stay within (perhaps not overloading transmission lines into Serbia/Kosovo)? – user253751 Mar 08 '18 at 09:53
  • @immibis: Chances are that due to the season, there's simply not enough solar available. Germany is phasing out nuclear and everyone is phasing out coal. Missing 80 MW is quite believable. – MSalters Mar 08 '18 at 11:18
  • 14
    **"The scary thing is that we're actually maxed out and can't find an extra 0.13%!"** This is presumably wrong. In fact nobody wants (or better wanted) to pay the extra power needed to balance things out. [Kosovo Govt to Pay €1m for Serbs’ Electricity](http://www.balkaninsight.com/en/article/government-pays-a-million-euro-for-electricity-bills-in-northern-kosovo-03-06-2018). It's rather a political problem than a lack of capacity. – klanomath Mar 08 '18 at 13:52
  • 1
    @MSalters Then you're saying it's a political problem caused by phasing out nuclear and coal? 20MW is - as a very rough approximation - 10% of a small power plant or 1% of a big one. As a sensible system operator you wouldn't allow your system to have less than one plant of spare capacity, otherwise any single failure would cause big problems! – user253751 Mar 08 '18 at 21:21
  • 2
    Most grids have a protocol to start more generation - when they were run by a single company, like the CEGB, this was people in a central control room. I assume that for political/commercial reasons, nobody is starting power plants (e.g. in Austria or Germany) to make up for the Kosovo/Serbia deficit. On a smaller network, this would lead to the whole thing tripping out, but because the ENTSO-E network is so large, it just decreases the frequency. – Rich Mar 09 '18 at 00:11
  • 1
    Another thought that occured to me - perhaps the slight frequency deficit is intended, in order to decrease energy exports to Serbia/Kosovo to the level they've paid for? (But that seems like a bad idea if it's going to mess with the whole rest of Europe. Better to disconnect them entirely if they refuse to pay...) – user253751 Mar 10 '18 at 02:56
  • 1
    There must be more at play here even technically. The continental synchronous area as a whole clearly did *not* approach it's maximum available power. And in absence of further regulation, the generators that are approaching maximum power would slow down a bit, fall behind in phase and that would reduce their load, allowing them to catch up. There *must* have been additional, explicit, regulation, side-effect of which was this overall reduction in frequency (if I understand right, the regulation would be forcing Kosovo slightly ahead in phase). – Jan Hudec Mar 10 '18 at 11:55
34

How a decrease in electricity production can lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?

Answered before: Why do generators have to rotate at a slower frequency if demand outpaces the supply?

If the loss of power from some countries causes a frequency deviation, shouldn't we also observe other impacts, like a drop of the output voltage? This means we've also been experiencing a drop of voltage for weeks here in Europe?

frequency reduction is primary the means to regulate, not voltage. But, yes, you'll see some amplitude (envelope) variation.

Why some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology? This means the same oven needs 2 different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.

Now coming to the relevant question:

Nope, these won't have firmwares the way you think. Also, you can't sell 100% the same oven in countries with different grid frequencies, anyway, because 60 Hz countries tend to use different grid voltages.

These clockkeeping circuits will more look like zero-crossing detectors (that is, a very minimal comparator with a cap on one input, fed directly from the power line, most likely through a resistive voltage divider) and counters, feeding a very minimalistic dedicated clock IC. We're talking low-tech here. Things produced in the millions where using a decades-old ASIC is cheaper than using a quartz + microcontroller.

Also, notice that with a minimal amount of additional complexity (an RC filter) it would be relatively easy to figure out whether you're running on nominally 50 Hz or 60 Hz, so not even your "needs to be different for different grids" argument works!

Marcus Müller
  • 88,280
  • 5
  • 131
  • 237
  • Marked as answered, but I still don't get why it hasn't been corrected by the rest of the grid shortly after the initial incident happened. Why did it last so many weeks with no action to protect client electric systems (oven clocks may not be the only impacted systems... some more critical ones may have been impacted as well?) Or was it only because of "non-technical"/people reasons? – Evariste Mar 07 '18 at 20:08
  • it's working as designed. While there is a slightly higher consumption than production, the frequency drops. If you decrease consumption or increase production, things go back to normal. What's so strange about that? – Marcus Müller Mar 07 '18 at 21:13
  • 5
    All good info but really does not explain why the grid controllers did not play catch-up on the frequency count. – Trevor_G Mar 07 '18 at 22:13
  • See [TIME ERROR CORRECTION](https://en.wikipedia.org/wiki/Utility_frequency) – Trevor_G Mar 07 '18 at 22:25
  • well, frankly, I kind of never understood why one would invest millions into keeping an arbitrary imaginary frequency counter steady over a long-term average, so maybe they just decided that this can wait till summer, when heating and light demand less energy. – Marcus Müller Mar 07 '18 at 23:25
  • 18
    In addition to being cheaper than a quartz crystal, the circuits are *more accurate*. I've got two clocks that use the powerline frequency for timekeeping, and two (a thermostat and a light switch) that use internal oscillators. The powerline clocks haven't drifted measurably in years, while the thermostat drifts by about 20 minutes a year, and the light switch drifts by 30. – Mark Mar 08 '18 at 02:39
  • ... I have exactly that argument with my father once every few months: nice, so your grid-controlled clocks are correct on a longish term, but have a lot of variance on short terms. It really depends on the quality of the oscillator, but I do not agree with *more accurate*. – Marcus Müller Mar 08 '18 at 06:30
  • 1
    Plus, as perfectly demonstrated by the issue at hand, the clock quality of your grid depends on systematic external factors, which are completely out of your control. – Marcus Müller Mar 08 '18 at 06:32
  • 4
    @Evariste I'm not sure why you marked this as the right answer when it didn't answer your main question. If I understand correctly, your question is why the net hasn't kept up with the frequency. It's customary to wait at least 24 hours before accepting an answer, to give time for everyone around the globe to answer, and to give time to write quality answers. – pipe Mar 08 '18 at 07:54
  • I always feel indebted to whomever has spent time for me. Also, we can easily unaccept at any time if a better anwser emerges. And finally, I hoped my comment asking for more clarifications on that specific point would be answered later on. I also don't want to throw a question and leave the forum as I can see too many times; often the OP simply disappears and we never hear from him/her again. In those cases, I feel uers who have taken time to answer are a bit fooled. Anyway, maybe this discussion would be better located on meta. – Evariste Mar 08 '18 at 09:33
  • 4
    Some stoves/ovens have mechanical clocks. Would they maybe use an AC motor that rotates in sync with the line frequency, geared down? e.g. the stove in my mom's kitchen has digital numbers that mechanically flip over. (Or at least they did until I set the time back 1 hour by turning the knob left, when I was 8 or something and didn't know that clocks were commonly made in ways that let the user easily destroy them.) Anyway, the thing might well contain no digital logic anywhere, just a mechanical clock and oven timer, and some circuits for power regulation based on dial settings. – Peter Cordes Mar 08 '18 at 10:18
  • The entire network of traffic signals used to run on a/c synchronous motors, as did most wall clocks. The accuracy of the powerline frequency as a timebase was a *service* provided to customers. Maybe it still is. –  Mar 09 '18 at 19:16
  • 2
    @Evariste The point of accepting an answer is to signal that the question is no longer in need of any more answers. The correct way to show gratitude in this case is with an upvote. Besides, a better answer now seems to have surfaced. – nitro2k01 Mar 09 '18 at 20:47
  • 3
    @Evariste even if I'm the one who wrote this very answer, the others are right - you should accept, and only accept, an answer that answers your question. I take your upvote with gratitude and do not hold any grudge should you unaccept my answer and accept a different one!! – Marcus Müller Mar 09 '18 at 20:52
20

How can a decrease in electricity production lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?

You can think of the electricity grid as being like a giant mechanism. Induction motors are like belts that can slip a bit. Synchronous motors and generators are like gears that cannot slip.

In the short term frequency is used to regulate the power flow in and out of the grid. If the grid is overloaded it will start to slow down and conventional generators will increase their power to compensate. Similarly if the grid is underloaded it will increase in speed slightly and generators will back off.

Eventually if the grid frequency gets too low then the grid will start dropping loads to prevent a complete collapse.

When the grid frequency drops below nominal, central control should command some power stations to increase their power set point so that the grid comes back up to its nominal frequency. Those power stations will need to be paid to increase their setpoints.

It seems that the political issues resolve around who should pay the power plants to increase their setpoints. If no one pays then the grid frequency remains reduced (and all the conventional power plants end up generating slightly more than they were contracted to generate).

Peter Green
  • 21,158
  • 1
  • 38
  • 76
4

To answer the "Why not quartz?" question:

Crystals are actually pretty terrible even for short-term timekeeping. A nice crystal on Digi-Key will typically have about 20 ppm accuracy.

$$1\ \mathrm{day} * 20\ \mathrm{ppm} = 1.728\ \mathrm{seconds}$$

But you probably won't have a nice crystal. Nice crystals don't sell consumer products. For example, the crystal in my wristwatch is about 66 ppm fast:

$$1\ \mathrm{day} * 66\ \mathrm{ppm} = 5.702\ \mathrm{seconds}$$

So after 12 days the watch is off by 1 minute. After a month it's off by ~2.5 minutes. 5-10 minutes (2-4 months) is enough drift to start causing problems. And that's not including temperature drift.

The power line frequency might not be more precise on a time scale of seconds or minutes, but the number of cycles per day is usually well-controlled. That's why the European grid issues made the news.

Adam Haun
  • 21,331
  • 4
  • 50
  • 91
  • 1
    The value of 5.072 is wrong, 5.702 is right, but it is not possible to change only two characters. – Uwe Mar 09 '18 at 21:40
  • @Uwe It is if you've got enough rep. Thank you for the correction. I need to proofread my answers more; I've been making a distressing number of errors. – Adam Haun Mar 09 '18 at 22:21
  • In the olden days, power grid was used for synchronizing events across remote locations. Nowadays (in the last 20 years) this kind of timing and synchronization is done using GPS. – Nick Alexeev Mar 09 '18 at 22:35
3

Why do some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology? This means the same oven needs two different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.

Because it is cheaper and still reliable (even more accurate?) then quartz crystal. And particularly the entire European continent is running on the same electricity network. So you can sell your oven to that total number of customers. For other countries manufacturers would make different versions anyway. There aren't many items that are sold everywhere (in every country) exactly the same.

polfosol
  • 227
  • 2
  • 8
roel
  • 131
  • 3