I have a question about a 3-phase 400V motor used by an hydraulic pump.
I read its currents and their graph is quite strange to me, far from the usual (deformed) wave.
I have a question about a 3-phase 400V motor used by an hydraulic pump.
I read its currents and their graph is quite strange to me, far from the usual (deformed) wave.
A motor like transformers has some excitation current that causes some <10% phase lead on current with respect to voltage (not given/shown.)
But what is shown is the current of each phase with a dominant 3rd harmonic current from the non-linear core ( partial saturation at peak voltage).
By hand drawing a similar sine wave with a 3rd harmonic and adjusting the phase and amplitude, I see that the 3rd harmonic is approximately 41% of the fundamental and the phase is 1.95 radians phase lead. Since reactance increases 300% with 3rd harmonic, we expect this for an inductor. But the core having partial saturation properties shows that the 3rd harmonic content is between 1/3 and 1/2 of the fundamental. THis is stored energy and not contributing to work by the motor. (VAR)
The pump load will also emphasize the current harmonics and sub-harmonics if a gear ratio is involved.(not observed or analyzed) as the load is not linear throughout the pump cycle.
The fundamental above is normalized to 1 @ 0 deg phase near 50Hz with the 3rd harmonic only shown in yellow with composite waveform in red.
You can see the website where to analyze FFT and settings that I used.