In the course I'm reading, there's this example to show that a low power factor leads to more current being drawn, and thus more power lost in the transmission lines.
Assume a certain load requires 1 kW to function correctly.
If the power factor were 0.9, and the power supply gives 110V, we would need 10A. If the power factor were 0.6, and the power supply gives 110V, we would need 15A.
However, something here just doesn't make sense. If we consider the power supply as an ideal voltage source, then the current has nothing to do with the given power.
It seems that he just assumed the load would draw the required power to function properly no matter what.
On the other hand, it seems to me that the current would stay the same, being affected by the impedance of the load, leading to a lower real power and thus a malfunctional load.
Where did I go wrong?
Hasan Saad
  • 161
    Have you learned about capacitors and inductors yet? – Tyler Oct 13 '17 at 18:00
  • Yes,I have done so. – Hasan Saad Oct 13 '17 at 18:04
    What do you understand by the term "power factor"? – Solar Mike Oct 13 '17 at 18:04
  • It is the ratio of the real power to the apparent power. My problem is not understanding how the power supply manages to increase the current as to deliver the required real power. If we considered it as a voltage source, it should not be able to supply enough power. – Hasan Saad Oct 13 '17 at 18:05
  • You should read up on what [reactive power](https://en.wikipedia.org/wiki/Volt-ampere_reactive) or, Q, is :) –  Oct 13 '17 at 18:07
  • I know what reactive power is, but that is not my point... – Hasan Saad Oct 13 '17 at 18:08
    Do not consider it as a voltage source, consider it as a power source. The fact that a load is taking it's peak current at a different time from the peak voltage means the generator needs to supply higher current to send the same amount of real power. – Trevor_G Oct 13 '17 at 18:12
    That's very well said @Trevor. Yes. Think of real power as your ideal power, what you're **supposed** to have if there was no induction or capacitance in your power... but that's not the case. –  Oct 13 '17 at 18:15
  • This is exactly my point, and other answers have answered completely different things. Is there such a thing as a power source that is able to supply more current just so that the load would take the required power? – Hasan Saad Oct 13 '17 at 18:15
    @HasanSaad pretty much every power supply does that, the current is dictated by the load..within the maximums of the supply. – Trevor_G Oct 13 '17 at 18:17
  • Well please write that as an answer. If you can, I'd like it if you explained how such a thing would be achieved. I mean how a supply would know that it has to deliver such and such power and change current accordingly – Hasan Saad Oct 13 '17 at 18:22
  • @HasanSaad Think of a DC power source driving a load with a capacitor. When the load does work, it drains the capacitor, forcing the power source to charge it again. Magically, the supply will know precisely how much power to supply to keep the capacitor charged, and it will perfectly equal to the power drawn off the capacitor to do work. Now just realize that the capacitor isn't doing anything magical and the argument works the same without it. – David Schwartz Oct 13 '17 at 19:01
  • @David I still find it hard to understand how the load can make a power supply draw additional current just so that it would meet its required wattage – Hasan Saad Oct 13 '17 at 19:06
  • @HasanSaad Try it this way: Imagine a load connected to an AC power supply. It's doing some particular amount of work. Now imagine we connect some capacitors and inductors in parallel with it. Do you agree that the power supply will see a different current flow? But do you agree that the exact same work will be done? Magically, as I mess with these capacitors and inductors however I want, the power supply "figures out" the right current to get the exact same work done. With the right combination of capacitors and inductors, current will be minimum. Then, PF will be 1. – David Schwartz Oct 13 '17 at 19:11
  • That magically and figures out is the point thats confusing me – Hasan Saad Oct 13 '17 at 19:14
  • @HasanSaad It's just trying to maintain its voltage. – David Schwartz Oct 13 '17 at 19:18
  • But it has a constant voltage, no? How would it need to maintain the voltage it produces? How would that be affected by the real power the load consumes? – Hasan Saad Oct 13 '17 at 19:22
  • Let us [continue this discussion in chat](http://chat.stackexchange.com/rooms/67083/discussion-between-david-schwartz-and-hasan-saad). – David Schwartz Oct 13 '17 at 20:59
8 Answers8
  • The in-phase current has everything to do with the power. \$ P = VI \$.
  • The out-of-phase current does not contribute to the power but does contribute to the overall current drawn from the supply. The increased current causes an increased voltage drop along the lines giving poorer voltage regulation at the load. This is a bad thing!
  • It will draw the required power and this will be measured in kW and billed in kWh.
  • It will also draw reactive power measured in kVAr and billed in kVArh. Typically the utility will charge for excessive kVArh.
No.
Links:
See my answer to How do capacitors improve power factor without destroying the capacitor?. It may help.
Simulation
Figure 1. A complicated struggle with CircuitLab's AC simulation capabilities.
Note that the values of L3, L4 and C2 have been chosen to have an impedance of 1 Ω at 50 Hz. The parallel R5-L3 pair should be out-of-phase by 45°. L4 and C2 should cancel out as their impedences are the same at 50 Hz. The 1 mΩ resistors are to help the simulator settle down after the initial transients.
Figure 2. The current waveforms for Figure 1. Note that the brown should be superimposed on the blue. The simulator is struggling.
  • The voltage plot has been omitted for clarity but the blue curve is in phase with it and will be taken as the reference.
  • The current for circuit (a), the resistor, is plotted in blue. As expected 1 V into 1 Ω gives 1 A peak.
  • The current for circuit (b), R5 and L3, is plotted in orange. Notice that the orange curve crosses the blue curve exactly at its peak (90° into the blue cycle). This occurs because the inductor current is lagging the voltage by 90° and is zero at this point. As the inductor current continues to rise the resistor current is falling. The peak occurs at 45° into the cycle where both currents are at \$ \frac {1}{\sqrt 2} I_{PEAK} \$. It follows that the peak of this waveform will be \$ \sqrt 2 \$ times that of the blue.
  • Finally note that if we add a capacitor of equal impedance to the inductor as in (c) the brown curve that we are back in phase again and the current has reduced. (I was expecting this to overlap the blue curve. I suspect the simulator is struggling.)
In summary:
  • The generator is constant (AC) voltage output.
  • The generator provides the current required by the load.
  • If the load is reactive (not purely resistive) the current increases while the useful power transferred remains the same.
  • By balancing the inductive and capacitive elements in the load the power factor can be brought back to unity.
Transistor
  • 168,990
  • 186
  • 385
Assume you had an ideal capacitor connected to your AC mains. It draws a current because it has an impedance of $$Z_C=\frac{1}{2\pi\cdot f\cdot C}$$ For example, a 1µF cap on a 230V, 50Hz mains draws $$I_C=\frac{U}{Z_C}=230\,\mathrm{V} \cdot 2\pi\cdot 50\,\mathrm{Hz}\cdot 10^{-6}\mathrm{F}=72\mathrm{mA}$$
This current leads to pure reactive power. The voltage is out of phase 90°, so there is no actual power, cos phi is zero, sin phi is 1.
$$Q_C=230\,\mathrm{V}\cdot 72\,\mathrm{mA}=16.6\,\mathrm{var}$$
Now connect a 40W incandescent light bulb in parallel. It has no reactive power:
$$I_B=\frac{P}{U}=\frac{40\,\mathrm{W}}{230\,\mathrm{V}}=174\,\mathrm{mA}$$
What is the current, in sum? The answer is
$$I=I_C + I_B=246\,\mathrm{mA}$$
And the appearant power?
$$S=U\cdot I=230\,\mathrm{V}\cdot 246\,\mathrm{mA}=56.6\,\mathrm{V\!A}$$
If you had the cap and the light bulb in a blackbox, know the voltage and could only measure the current, what would you tell it is?
Janka
  • 13,636
It is ok to consider power supply as an ideal voltage source, but the current has everything to do with the given power. The characteristics of the load dictate what the current and power factor will be with a given supply voltage. An ideal voltage source will do whatever is necessary to accommodate that demand without changing the voltage.
A load that is composed of resistors capacitors and inductors with a given applied voltage will draw a specific current at a specific power factor. The power factor will not change unless something is added or subtracted from the load. That change could be a malfunction or it could be a normal change in the load.
An induction motor load can be modeled as some inductors, a transformer and some resistors. The mechanical load is modeled as a variable resistor. If the mechanical load changes, the power factor changes due to the change of the variable resistor. There is also a small change in power factor due to a change in the proportion of current in the inductive components of the circuit. That is a normal change not a malfunction.
The an increase in the reactive portion of the load does not cause the generator to work harder except to the extent that the losses increase due to the increased current. Reactive power is energy circulated continuously between the load and the source. The prime mover needs to supply only the losses associated with that energy circulation.
  • How does the generator react to that loss? I mean, how would it know that such and such was lost and the prime mover needs to work harder so that it would make up for the loss? – Hasan Saad Oct 13 '17 at 19:15
  • Just as described by @Trevor "That drawn power tends to brake the generator, and the generator then consumes more power from the prime mover to work harder to keep up to speed." The generator requires more torque to continue at the same speed, so the voltage regulator opens the throttle to keep the engine speed from dropping. –  Oct 13 '17 at 19:37
  • I have no idea of the inner workings of a generator. Is it safe to assume that it will provide a constant real power and will change the current accordingly? Are these topics such as voltage regulator and torque of a generator etc beyond the scope of this question? – Hasan Saad Oct 13 '17 at 19:40
    The generator will provide a constant voltage and frequency. The load determines the current drawn and thus the power. The current will provide the power drawn by the load within its capacity. If the capacity is exceeded, the generator may no longer be able to keep the voltage and frequency constant. It may overheat and the prime mover may overheat. Protective circuits and devices may disconnect the load or shut down the generator. The regulator controls both the throttle and the generator's field excitation. The details are beyond the scope of the question. –  Oct 13 '17 at 21:18
This is a short answer, so I'm sure another one will come along soon with nice diagrams, but:
In an ideal situation, the current and voltage wave forms are in sync (power factor 1). This gives a power of X. If we take those same exact waveforms and start to shift them out of sync, the power level will decrease. If we need the same power (x), with the warriors out of sync, we need to increase either the volatge or the current. We usually want to keep voltages constant, so instead we increase the current. This means that, as wave forms go out of sync (I.e. the power factor decreases), we need to up the current to keep the power the same.
Edit: oops, a minute late
BeB00
  • 5,303
  • Leave it. It's a different approach to mine. Let the OP decide! – Transistor Oct 13 '17 at 18:15
  • "we need to up the current to keep the power the same." I might reword that, the generator needs to work harder to deliver a higher current. It's not like the current is adjusted per-se. – Trevor_G Oct 13 '17 at 18:15
  • Yeah I wondered about clarifying that it's not an action taken at the generator side, but then I felt that it's a quick explanation, and it's not false, it's just not talking the whole story, so it was OK. – BeB00 Oct 14 '17 at 18:59
At any moment in time, the amount of power being transferred through the wires between a source and a load will be the instantaneous voltage times the instantaneous current. If a device has a power factor of 1, all power that is transferred will be consumed by the load. If a device has a power factor of zero, all of the power that is transferred to the load during one part of a cycle will be stored and then transferred back to the source during another part. If a device has a power factor between zero and one, some of the power that goes through the wires will drive the load, but some will be stored up and fed back through the wires.
Power which flows from the source to the load and back on each cycle won't do any useful work, but the current will still flow through the wires in the process of transferring that power. Transferring a given amount of "useful" power will require transporting enough current to carry that, plus additional current to transfer the power that keeps going back and forth.
supercat
  • 45,939
  • 84
  • 143
Here's an analogy: If you're working behind a cash register the most efficient transaction is when everyone pays the exact amount in cash. That's power factor 1.
If everyone needs change the transactions are less efficient even though the accounting ends up the same. That's power factor less than one.
On the transmission line, the extra current isn't consumed, it "resonates" on the line where it generates parasitic I^2R losses and makes the transmission line less efficient.
Steve Ravet
  • 106
Instantaneous power is voltage times current. The voltage defines the potential difference a current has to be put through: it's like some water current: the current does not eat or deliver energy as such until you look at the height difference you want to cross.
With a pure resistive load, the current is proportional to the voltage. Now we are talking about AC here, so the voltage and current and instantaneous power change all the while. When they are in synch, the total energy needed for a longer amount of time is maximized. When they aren't in synch, the load is not purely resistive (which would make it dissipate power). Instead, there is inertia involved which then stores energy momentarily and gives it off later. The voltage source no longer only delivers power but has moments where its current and voltage have different signs and thus it receives energy back that it has put out previously.
In the extreme, a load factor of 0, voltage and current are out of synch by 90 degrees and no energy is actually consumed but only pumped back and forth. The water equivalent is a pail of water on a swing: it passes back and forth and changes height, but its direction and its height are out of phase, so no actual energy is converted into heat.
Now any wires are basically resistive and the voltage across them (rather than between them) is in synch with the current through them. So they incur just the same amount of power loss at the given current as if the power factor were 1. At the same point of time, you only pay for the power loss inside of your home: the losses outside are not metered.
One can actually use large synchronous motors as capacitors or inductors depending on how large you make the electric field of the rotor. The energy is stored here in the rotating mass, so you want a bit of mass on the axle, and you want the machine to be able to deal with the resulting torques and angular vibration.
The fact that a load is taking it's peak current at a different time from the peak voltage means the generator needs to supply a higher current to send the same amount of real power.
The generator does not know it has to deliver such and such a power, the load pulls whatever real power it needs. That drawn power tends to brake the generator, and the generator then consumes more power from the prime mover to work harder to keep up to speed.
Trevor_G
  • 46,364
  • 68
  • 151
  • No, the generator has absolutely no understanding of the power it is required to provide. A generator provides a regulated voltage, it tries to keep that voltage constant. The current drawn at any point in the AC cycle is defined mostly by the load and only limited should the generator be incapable of providing the required current due to a magnetic limitation. – Jack Creasey Oct 13 '17 at 19:34
  • Yes @JackCreasey but if you load down the generator, take more power, doesn't it transfer more power to keep up the voltage. – Trevor_G Oct 13 '17 at 19:39
    A modern generator typically consists of two control subsystems 1) a voltage regulator which controls the base field current 2) a frequency controller to set the motor speed. In operation the speed control may even be mechanical (as it is in most simple power sources). The voltage regulator does not control the generator throttle. Increase the load (power) and the voltage drops (called controller droop), the voltage regulator increases the field current, but the speed is also reducing since we are taking motive power. The drop in frequency cause the throttle to open. No I or P sensing. – Jack Creasey Oct 13 '17 at 20:02
  • @JackCreasey I did not say it sensed it, rather that it self balances. The OP was specifically asking how the generator adjusts to add more current on demand. What you are saying and what I am trying to say, is the same thing. THough you explained it better. – Trevor_G Oct 13 '17 at 20:05