1

Typical distribution system can be illustrated as:

enter image description here

Here are my premises (and assumptions):

1-) Chassis in a house must be connected to the earth, not to the neutral.

2-) The earth and the neutral are connected together at the substation.

Imagine one lives in a house and there is no earth in the outlet. I have seen such apartments and never understood how they are allowed to wire houses like that.

Including this web-site, I encountered similar questions (so this might be duplicate but the reason is I didn't comprehend the given answers such as this one) but never understood one thing. And here is my question:

Is there an "easy" example showing the fact that connecting the neutral to chassis is a bad idea? An illustration of a scenario helps a lot.

clabacchio
  • 13,481
  • 4
  • 40
  • 80
floppy380
  • 1,715
  • 7
  • 33
  • 67
  • First which country are you working in? If the UK then all the earthing requirements are detailed in the wiring regulations 17th edition, and most countries have an equivalent. – Solar Mike Jul 13 '17 at 18:07

4 Answers4

2

As others have mentioned primary reason is earth/ground line is a backup line separate from the neutral line to provide two fault protection.

That is, more than one thing needs to fail. For a grounded chassis device the chassis can become live only if two (or three faults occur).

Two fault case: Earth connection broken AND Live wire shorted to chassis.

Three fault case: Earth connection broken AND Neutral wire shorted to chassis AND Live-Neutral reversed at outlet.

There is actually a single fault case too though.. "Earth pin is wired to live at the outlet..." but there is nothing you can do about that one...

Also, under normal circumstances the earth line should have zero current flowing through it. That is quite different from the neutral line that can have 10s of amps running though it which can produce significant voltage drops at various points along the conductor. The ground line "SHOULD" be at zero potential everywhere.

By the way, the wiring you show for House#1 is not legal in these parts. A separate ground is required at the residence, usually clamped onto the incoming water line if it is a metal pipe, or to a long ground spike. Neutral may or may not be tied to this ground at the fuse box. This provides better local protection as opposed to relying on the electric company and the integrity of the service which may get disrupted (torn down) during a storm.

Is there an "easy" example showing the fact that connecting the neutral to chassis is a bad idea?

Yes, it is unfortunately very easy and common for bad wiring to exist where line and neutral are reversed at the outlet. Most appliances don't care, but if you plug your device with the neutral tied to the chassis into such an outlet.. well you can figure out the rest.

Further there is the broken neutral line scenario which can also be quite lethal. Consider the drawing below.

schematic

simulate this circuit – Schematic created using CircuitLab

Lets assume appliance 4 used the neutral to ground the chassis. Since neutral does not actually go anywhere the chassis is really floating.

However, what happens when you turn on appliance 5. The neutral line coming out of appliance 5 is then pulled up to the live rail. Appliance 4s chassis will also become live. Appliance 5 could be in another room on the other side of the house...

Imagine one lives in a house and there is no earth in the outlet. I have seen such apartments and never understood how they are allowed to wire houses like that.

Standards vary around the world and age makes a big difference. People seem to forget that residential electricity is a relatively new phenomenon. In the early days things were A LOT more dangerous. It is only through time that we have developed more common and safer standards. Though, as I hinted, some parts of the world are still rather lagging due to the costs to replace everything... Canada/USA for instance, where you can still stick a plug into an outlet while touching the live pin....

Trevor_G
  • 46,364
  • 8
  • 68
  • 151
  • If line and neutral are reversed at the outlet and neutral was chassis grounded, in that case circuit breaker will trip. Please see the answer of the user Transistor and see my last two comments under that answer, you will see what Im asking for. Broken neutral is no more superior argument than broken ground. Thats the point I dont get. – floppy380 Jul 13 '17 at 18:55
  • @doncarlos no I meant with no ground. That's why you can't use neutral as a virtual chassis ground. You can't rely on it actually being neutral. – Trevor_G Jul 13 '17 at 18:59
  • yes I got it by saying neutral was chassis grounded I meant neutral was wired to the chassis no earth ground. – floppy380 Jul 13 '17 at 19:00
  • 1
    @doncarlos if the chassis is earth grounded, you need two (or three) faults to occur for the chassis to be live. 1. earth wire broken, 2 Live wire shorted to chassis. Or 1. earth wire broken, 2. Neutral shorted to chassis, and 3 Plug reversed. – Trevor_G Jul 13 '17 at 19:01
  • @doncarlos if you have no earth line, you need to rely on double insulation instead..... and cross your fingers. – Trevor_G Jul 13 '17 at 19:03
  • Woow I got it now. The probability gets less if we use earth since we need more events occur at the same time. – floppy380 Jul 13 '17 at 19:03
  • @doncarlos exactly :) – Trevor_G Jul 13 '17 at 19:04
  • I will accept your answer since that was what I coundt figure out – floppy380 Jul 13 '17 at 19:04
  • 1
    @doncarlos thanks. I expanded it a bit to explain the two fault protection idea a bit more clearly too. – Trevor_G Jul 13 '17 at 19:10
  • Your illegal house#1 wiring is actually de rigueur these days in the UK. We earth to the armour on the incomer. – Paul Uszak Jul 13 '17 at 20:33
  • @PaulUszak ya that's probably fine in the UK where most services are underground. Over here a lot of it is still arial. – Trevor_G Jul 13 '17 at 20:35
0

I have seen such apartments and never understood how they are allowed to wire houses like that.

They are not allowed to, and haven't been for ~50 years (in my jurisdiction), but many houses are more than 50 years old.

Is there an "easy" example showing the fact that connecting the neutral to chassis is a bad idea?

Just as an example, if the neutral wire returning to the panel gets broken, you'd get return current going back through the ground wire and not notice the fault. Then when another fault happens (broken ground wire), you would end up with a hot chassis.

The Photon
  • 126,425
  • 3
  • 159
  • 304
0

I wrote the linked answer. Here's a variation of the illustrations in that answer.

schematic

simulate this circuit – Schematic created using CircuitLab

Figure 1. Device has had neutral wire connected to chassis.

I have added a fault to the wiring. The neutral cable is broken.

Now consider what happens when someone switches the light on. The top of the bulb goes live as does the bottom and the chassis. This is an electrocution risk.

Even when the neutral is OK there is still a problem. With normal currents flowing there will be a voltage drop along the neutral cable meaning that the chassis will be several volts above ground. Touching the chassis and a properly earthed device or steel sink / plumbing will cause a current to flow through the body. Again, this is potentially fatal.


Comments

But now do the same thing with the usual case i.e. with the chassis properly connected to the earth. Now in proper case imagine the live touches to the chassis; and imagine also now the earth wire is broken. Now we have the same situation in your first example. What's the difference?

  • Two faults are required to create the danger. In my Figure 1 a dangerous situation could occur with a single fault.

Neutral wire broken we have problem. Earth wire broken we have problem. Why to prefer still earth to neutral?

  1. Because of the voltage drop across the neutral return wire. This is a serious enough concern on its own. The problems caused by this would vary from not noticeable through ticklish to fatal.
  2. We wish to maintain the chassis at earth potential so we use a dedicated wire which does not carry any current except in the case of a fault.
  3. Your RCD/GFCI would not be able to detect a fault in your scenario. These devices offer additional protection in these cases.
  4. Separation of power and protection circuits.

In industry in Europe it is a requirement to test earthing periodically on certain equipment. For example, the PAT (portable electrical test) units will test earth continuity and insulation. These periodic tests are designed to catch the missing / broken earth fault before a second fault can cause a problem.

Transistor
  • 168,990
  • 12
  • 186
  • 385
  • Let's ignore the secondary reason and focus on the first reasoning. I see your point you imagine the neutral wire is broken... But now do the same thing with the usual case i.e. with the chassis properly connected to the earth. Now in proper case imagine the live touches to the chassis; and imagine also now the earth wire is broken. Now we have the same situation in your first example. What's the difference? – floppy380 Jul 13 '17 at 18:21
  • Neutral wire broken we have problem. Earth wire broken we have problem. Why to prefer still earth to neutral? – floppy380 Jul 13 '17 at 18:24
  • See the updates. – Transistor Jul 13 '17 at 19:34
0

A fundamental principle of safety is that a single "plausible" failure should not in and of itself create an immediately-dangerous condition. If the case of a device is attached to the panel ground via one route (the groundING conductor) and the power that flows through the device returns to the panel via a different route (the neutral, groundED conductor), it will not be possible for a dangerous voltage to appear on the case unless one failure causes a something to be connected to the case that shouldn't be, and another failure causes the case not to be connected to ground.

If a proper groundING conductor is not available at an outlet, danger may be minimized by installing a device which in the US is called a Ground Fault Circuit Interruptor (GFCI) and in other countries is called a Residual Current Detector. When an electrical device is working normally, almost all of the current that flows through the hot conductor will return to the panel exclusively through the neutral conductor. Most electrical-shock scenarios, by contrast, involve current which flows out through the hot wire but returns to the panel through another path. A GFCI senses the difference between the amount of current flowing in the hot and neutral wires, and will break the circuit within about 1/50 of a second if they don't balance. If a fault would cause the case of a device to be erroneously connected to "hot", that might not trip a GFCI if no current flows, but if someone were to touch the case while it was live, a GFCI would likely trip fast enough to prevent the resulting shock from being lethal. Not a wonderful situation, to be sure, but a less dangerous situation than would exist with no protection.

supercat
  • 45,939
  • 2
  • 84