I have the above mechanism, where I control a single-phase fan motor's switch. I mean instead of a mechanical switch, an AC/DC SSR is switching ON or OFF from a remote place by a constant DC input (DC in in figure, 10V or zero). When the SSR is ON, it will stay ON for long time like an hour or more. I mean it is not for speed controlling itself, it should act just to turn on the fan or turn off. The speed controller in the figure is an AC phase controlled speed controller(like a dimmer for inductive loads).

Here is the speed controller regarding the above figure: http://uk.rs-online.com/web/p/fan-speed-controllers/6685345/

As you see in my illustration when the SSR is ON, the hot line is connected to the speed controller. The fan speed is controlled via the poti knob of the speed controller manually.

The system above works for tests until now with the following SSR (Of course I cannot see whether there are current spikes or surges during each switching). Here is the SSR with zero crossing I have and use currently: http://uk.rs-online.com/web/p/solid-state-relays/2181959/?origin=PSF_428032|alt

The data-sheet says "Switching Type: Zero Crossing" and "Output device: SCR"

*But I started to get worried when I read the following articels:

http://www.jelsystem.co.jp/en/product/ssr/ssr_dosa.html

http://www.crydom.com/en/tech/newsletters/solid%20statements%20-%20ssrs%20switching%20types.pdf

*They claim a zero-crossing SSR is not recommended for an inductive load.

My question is:

1-) Do I need a random-fire SSR instead of a zero-crossing one considering my illustration and the articles I read? I'm asking becasue I thought the speed controller would be taking care of dV/dt effects even I use the zero-crossing one. But I'm not sure its effect on the SSR's SCR or triac if I use the one I have with zero-crossing.

Here I found a random-fire switching type below:

http://uk.rs-online.com/web/p/solid-state-relays/4092851/

Its data-sheet says "Switching Type: Random" and "Output device: Triac"

Which one would you recommend in my case?

2-) This is a bit confusing for me because I cannot find any wave forms of the inner trigger circuitry(the part which triggers SCR or the triac) when there is continuous DC input for lets say minutes or hours.

What I understand until now when there is zero-crossing, the circuitry detects zero crossing points and fires each time when the voltage crosses zero point. So what I understand is that, in one second for a 50Hz AC, the SCR fires 100 times if the DC in is constant and ON for one second . Is that right?

If above is true, my question is about the random-firing SSR. Okay in zero-crossing case the SCR detects and knows when to fire. But how about random firing case?

How is the triac inside the SSR is fired? What does firing it randomly means if the DC in constant ON all the time? How often it fires in this case and would that create some surges? Or in constant DC in case the triac is always on and there is no firing? The confusion arises because a triac is not a transistor and unlike a transistor it will not be ON when its gate is always ON right? I struggled to find an answer but I failed and had to write as a question.

I would be very glad if you can illustrate the wave form in this case.

Edit: Some simulations with LTspice:

Here is an opto-triac with zero crossing:

As you see below the opto-triac fires at each zero crossing point when DC in is 5V constant all the time. I'm asking is that the same case in zero-crossing SSRs?

enter image description here

Figure 2.

And below is an opto-triac this time with no zero crossing and DC in is always ON again:

enter image description here

Figure 3.

As you see above the opto-triac again fires at each zero crossing. What is going on here? It is not random.

Another example here. And this time again we have an opto-coupler with no zero-crossing "with an inductive load":

enter image description here

Figure 4.

And here an opto-coupler with zero-crossing "with an inductive load":

enter image description here

Figure 5.

Edit 2:

A non-zero cross optocoupler

enter image description here

user16307
  • 11,802
  • 51
  • 173
  • 312
  • See my answer to [Confusion with TRIAC firing and zero crossing point](http://electronics.stackexchange.com/questions/232921/confusion-with-triac-firing-and-zero-crossing-point/232959#232959). Ask for clarification on any point here. – Transistor Jun 02 '16 at 17:45
  • @transistor in the previous question you linked and explained there you show the output wave-forms in case of zero crossing and without zero crossing when there is on off type heat regulation. i understood that. but now i cannot picture when DC in is "always ON" how is the triac is triggered inside the IC? so i have 2 issues here. 1-) in zero-crossing case when the "DC in always ON" how are SCRs triggered inside IC? 2-) in random-firing SSR when the "DC in always ON" SSR how is the inner triac is triggered in time? and lastly which SSR for my application better regarding inductive load issue. – user16307 Jun 02 '16 at 18:45

3 Answers3

5

If your circuit is working OK it will probably keep working OK. Some SSRs give trouble with large inductive loads as the current lags the voltage. If your fan is less than a couple of hundred watts you should be OK.

schematic

simulate this circuit – Schematic created using CircuitLab

Figure 1. Random SSR and zero-cross SSR.

  • The random SSR usually uses two triacs. The first is a small photo-triac. When the LED is turned on the photo-triac will turn on and feed current to the gate of the power triac and turn it on. R1 shunts away any leakage current to prevent false triggering. If the LED is kept lit this SSR will turn on after every zero-cross and stay on until the next one. If it is turned on mid-cycle it will turn on immediately.

enter image description here

Figure 2. "Random" or phase-controlled dimming.

  • The zero-cross SSR uses the same LED opto-isolation arrangement but usually turns on a transistor. This will pass current to the triac only when the voltage across the triac is close to zero. See Using AC current to trigger Triac for details on the inner working if the zero-cross circuit.

enter image description here

Figure 3. Zero-cross circuit being switched on and off. Note the full half-cycles.

  • In all cases the triac will remain on until the current falls to zero at the next zero cross or the power is switched off elsewhere.

Note that SSRs are not "integrated circuits" in the sense of "all on one chip". If you prefer, they are packaged circuits using multiple components, usually potted into a mini-case.

Your questions

Okay in zero-crossing case the SCR detects and knows when to fire. But how about random firing case?

Your control circuit tells it when to fire. This generally requires zero-cross monitoring so that the trigger signal timing is referenced to the zero-cross point.

How is the triac inside the SSR is fired?

Answered above. Opto-coupling.

What does firing it randomly means if the DC in constant ON all the time?

If DC is on all the time the triac will be triggered after every zero-cross.

How often it fires in this case and would that create some surges?

No because after the first cycle it is turning on at zero volts. This is the least stressful for the triac.

Or in constant DC in case the triac is always on and there is no firing?

It will fire.

The confusion arises because a triac is not a transistor and unlike a transistor it will not be ON when its gate is always ON right?

Links

"Random" SSRs"

"Random" is a misnomer as usually the trigger point is anything but random and is controlled. What is meant is "variable" trigger-point.

In your Figure 2 the DC is on all the time. As the AC voltage across the U2 rises the zero-cross circuit hasn't shut off the trigger yet. The blue trace shows the current into triac U2. Once it reaches the trigger value the triac switches on, the voltage across it drops to (almost) zero so the trigger current drops to zero. The triac keeps on conducting as is its nature.

In your Figure 3 the triac turns on as soon as possible after the zero cross. It's pretty much the same as Figure 2.

In your Figure 4 I can't make out where V[n002] is referenced but it's obviously out of phase with the voltage across the triac as the current through R1 is proportional to that.

Again, I'm not sure what you're showing in the Figure 5 trace.

More questions - comments on those you asked Richard Crowley.

1-) Does that really fire 100 times a second for a 50Hz AC?

Yes.

2-) About random-fire SSR case when DC in is always ON: How many times will the inner triac fire randomly? how would be the waveforms?

It's not "random". It's variable phase angle. Your control circuit decides when to turn on the LED. If you want 50% power you have to detect the zero-cross and wait 5 ms every half-cycle before triggering. The waveforms will be as in my Figure 2.

Comment to me:

What I understand is that if I use "random-firing SSR", I will still have fine AC but the very first cycle could be problematic. Is that right? Since the rest will fire at zeros as you said?

Correct although "problematic" might be overstating it. Zero-cross generates minimum noise, transients, electromagnetic radiation and is easiest on the triac and load.

Opto-triac only

enter image description here

Figure 4. From OPs link in comment.

In this simple circuit the LED is continuously powered. The opto-triac is in continuous conduction (once the voltage has risen high enough for it to turn on). It is behaving like a simple switch. The blue waveform is the current through the load.

In more normal use the opto-triac is wired across the power triac as shown in my Figure 1. As soon as the power triac is turned on there is (almost) no voltage across it anymore so no current flows through the opto-triac series resistor after the trigger "works".

Try dropping the excitation down from 230 V to 6 or 12 V and the resistor to 100 \$\Omega\$ or so. You should see that there is no current until the voltage is high enough to trigger the triac. This happens on the 230 V too but much sooner and the resolution of your chart isn't enough to see it.

Transistor
  • 168,990
  • 12
  • 186
  • 385
  • please see my edits. i hope i clarified what im asking about. – user16307 Jun 02 '16 at 19:38
  • Do those LTspice simulations represent SSR cases in my question? Because I used opto-triacs instead. Can I rely on those waveforms in the simulation? – user16307 Jun 02 '16 at 19:41
  • What I understand is that if I use "random-firing SSR", I will still have fine AC but the very first cycle could be problematic. Is that right? Since the rest will fire at zeros as you said? – user16307 Jun 02 '16 at 19:45
  • See the updates. – Transistor Jun 02 '16 at 20:54
  • I have problem to explain the behavior of opto-triac. I was thinking it triggers every half cycle itself. But without a power triac it does nothing. Please see: http://i.stack.imgur.com/0PlP9.png How can we describe in a simplistic way? In a way that such as: It sees the voltage and since it is connected to triac gate ect. Since I dont know that I cannot grasp what is going on. And that creates all my confusion. – user16307 Jun 02 '16 at 22:27
  • 1
    More updates. Once the power triac turns on there is no voltage across it so the trigger current falls to zero. – Transistor Jun 02 '16 at 22:50
  • If you illuminate the LED inside the opto-isolator with a constant DC voltage, then the photo-SCR receiver is ALWAYS "triggered" (ON). So, when the mains voltage passes through the zero crossing, the opto-isolator photo-SCR conducts mains voltage (100s of volts) into the gate of the main SCR. It takes very low voltage to actually cause the main SCR to conduct. So very very early in the cycle, the main SCR is triggered and remains conducting until the next zero-crossing. Rinse and repeat. – Richard Crowley Jun 02 '16 at 23:00
  • I'm looking at your Figure 1 Random SSR. Let me write how I understand what you wrote: I will try to write step by step what I can understand is happening. We assume D1 turns ON and remains always ON. DI1 becomes conductive which means it allows current in both ways positive and negative. TRI1's gate is connected to R1, when currrent passes down V1 is developed at gate. Because of a voltage V1 developed at the gate of TRI1 this turns ON TRI1. TRI1 will be ON until the end of the first positive cycle of AC mains than it will stop conducting...cont – user16307 Jun 02 '16 at 23:25
  • But now just after the AC alternates to the second cycle, DI1 will see a reverse current and again there will be a voltage -V1 developed at the gate. This -V1 at the gate will turn ON the TRI1 again. There will be very small delays very near to zeros because DI1 needs some small treshold voltage across. Did I understand it? – user16307 Jun 02 '16 at 23:25
  • I think you've got it. – Transistor Jun 03 '16 at 06:04
2

If you were attempting to create an additional speed control with your SSR plus the ebmpapst speed controller box, then you might have a problem.

HOWEVER you are using your SSR only as an ON/OFF switch. So none of the warnings in those sources apply specifically to YOUR circuit. But congratulations for doing due diligence and investigating possible problems. Kudos.

You can use EITHER type of SSR (Zero-Crossing or Random-Fire) because you are implementing only a "static" ON/OFF function. The Zero-Crossing SSRs seem much more readily available than the Random-Fire kind.

The Zero-Crossing SSRs have extra circuitry which "delays" your trigger signal until the NEXT zero-crossing. Otherwise they would fire ANYWHERE, even in the middle of the wave. (Which is what "Random-Fire" means). We would want to use "Random-Fire" SSRs where we were doing something like incandescent lamp dimming etc.

When you apply a constant gate signal to the SCR it simply "stays on" through all the zero crossings. In one sense, you could say that it "fires" again at every zero-crossing, but in fact it makes no difference one way or the other.

Richard Crowley
  • 14,382
  • 2
  • 20
  • 37
  • 1-) You wrote about zero-crossing SSR case when DC in always ON: ""In one sense, you could say that it "fires" again at every zero-crossing"" Does that really fire 100 times a second for a 50Hz AC?... 2-) About random-fire SSR case when DC in is always ON: How many times will the inner triac fire randomly? how would be the waveforms? – user16307 Jun 02 '16 at 19:06
  • The waveform for an SCR that is always triggered looks exactly like the incoming waveform. The gate is already "ON" when the waveform passes through zero, so it is only semantics that separate "always on" from "triggers at every zero-crossing". As they say: "It is a distinction without a difference." i.e. it doesn't matter what you call it, it behaves the same. – Richard Crowley Jun 02 '16 at 19:24
  • please see my edits. you will understand what im asking about – user16307 Jun 02 '16 at 19:37
  • I do not believe your simulation of DC/always on is correct. Specifically I don't believe the gate waveform is only a momentary spike as shown. But more importantly I cannot see why it makes any difference? – Richard Crowley Jun 02 '16 at 19:48
1

A zero crossing relay is fine in this application. The relay remains on once it is turned on, so it is not repeatedly fired. The internal zero-crossing detector is only used to reduce surges that can occur if the switch were turned on or off when the current is high. By switching at the zero point, the instantaneous current is zero at the time the switch is closed. But the switch stays closed once it is switched.

The reason you should not use it on large reactive loads is that the voltage and the current are not in phase, so the voltage zero crossing point is not the zero-current point. You might get a small "kick" when you shut off, which will be snubbed by internal snubber circuitry. The snubber has a resistive element which absorbs the energy. If you were turning on and off repeatedly, the snubber might get warm, but in your application there will be no issue.

John Birckhead
  • 10,524
  • 1
  • 11
  • 27
  • "The relay remains on once it is turned on"? I dont get that. Why does it turn off then when Dc in is zero? It looks to me DC in all the time has effect on triggering. And I thought it was triggering at every zero-crossing point to create a fill sinusoidal AC output. I didnt get this. – user16307 Jun 02 '16 at 19:02
  • When you put on the DC signal, you are energizing a photo isolator and the SCR is turned on next zero crossing. It then stays on as long as the DC signal remains. When you remove the DC, the opto-isolator is off and it will turn off the next zero crossing. – John Birckhead Jun 02 '16 at 19:17
  • See See http://www.bristolwatch.com/ele/triacs2.htm – John Birckhead Jun 02 '16 at 19:20
  • check my edit to my answer. you will understand what im asking about, more edits will come. – user16307 Jun 02 '16 at 19:26
  • The solid state relay conducts in both directions (positive and negative current) just like a mechanical relay when you apply the DC voltage to the control circuit. The zero crossing only refers to when the switch closes (or opens). So when you apply a control voltage, the relay waits until a zero crossing and closes and remains closed. When you remove the control voltage the relay waits until a zero crossing and opens. The delay is only a part of one 60Hz cycle on each end. In your simulation, are you driving the control input with an AC signal? It should be a control signal. – John Birckhead Jun 02 '16 at 20:43
  • No the control input is 5V constant DC – user16307 Jun 02 '16 at 20:59