1

Having trouble understanding this ladder logic program. I can solve more basic ladder logic programs but I do not know how to account for small voltage adjustments. Here is the problem:

You are designing a PLC program which controls a cooling van on a vehicle engine. The engine must stay at 205 degrees F. The PLC should have 2 outputs for fan control: an output which turns the fan on and off, and a second output which is a voltage value which corresponds to the speed of the fan. The fan speed voltage should be between 0 and 5 volts, where 0 V indicates a slow fan for 1 degree above temperature (206 degrees) and 5 V indicates maximum fan speed for 10 degrees above temperature (215 degrees). The input to the PLC is a thermopile which is 0 V at 150 degrees F, and increases by 25 mV for every degree F above that. The system should also have a third output which is an overheat light which flashes if the engine temperature ever reaches 15 degrees above the temperature setpoint (220F).

user3042929
  • 11
  • 1
  • 2
  • 1
    Welcome to EE.SE you may want to review the guidelines on asking questions and edit your question, because you have not actually asked a question, you have only stated a problem. http://electronics.stackexchange.com/help/how-to-ask – Voltage Spike May 11 '16 at 17:15
  • 1
    Also state the PLC make and model (and provide a link) so that we know what features are available. Post all this information **in your original question** and not in the comments. – Transistor May 11 '16 at 17:45

1 Answers1

2

Without knowing what PLC you are using, I'll give you an example with a CLICK PLC. The CLICK PLC makes this trivial as it has built in I/O on the processor and I'm using model C0-02DR-D $139 which has

  • (4) 24VDC inputs
  • (4) Relay outputs
  • (2) Analog inputs (configurable as 4-20mA or 0-5V)
  • (2) Analog outputs (configurable as 4-20mA or 0-5V)

The first thing is to scale the input. Some PLCs such as Allen Bradley's have instructions for doing this, but the CLICK makes this easier using a graphical editor. Here it is;

Click PLC analog input scaling

The temp input signal is connected to input AD1 (analog to digital). We select 0-5V option. For scaling we set 0V = 150deg F and 5V = 350deg F (since 25mV = 1 degree).

5V = 5000mV   
5000mV/25mV = 200
150 + 200 = 350

The scaled input is saved in memory register DF1 which is a 32 bit floating value address.

Now we scale the output;

Click PLC analog output scaling

The output fan speed output is connected to output DA1 (digital to analog). Again, we select 0-5V option. 206deg F = 0V and 215deg F = 5V. For this output, we assign memory register DF3, a 32 bit floating value address. Notice on both Input and Output scaling, we selected the option Enable Range Limiter which tells the CLICK to ignore values outside of the limits.

Here is the Ladder logic. I included comments for explanation

Click PLC fan control

As you can see, it took only 7 lines of PLC code. I do this for a living, so I find this trivial. Good luck!

CORRECTION: On comment of line 3 in the ladder, I meant to say copy value of DF1 into DF3 not DF2.

Moses Machua
  • 141
  • 4