I have the following setup:
480V, 200A service fed into PWM Drive, Drive output going to 1000kVA step up transformer (8.4 ratio) feeding a 2380V/53A 3phase induction motor. The motor is UNLOADED.
When running at NP, I measure (with multiple devices) 477V/28A into my drive input. I measure roughly .65 pf
However, I push 283V/158A out of my drive to reach my NP motor voltage and current requirement. I don't have a PF but I imagine it's somewhere in the .13 range.
S = sqrroot(P^2 + Q^2) P = VIcos(theta) Q = VIsin(theta) (might be forgetting the 3)
IN P = 8681W Q = 10079VAR S = 13302 VA
OUT P = 5812W Q = 44278VAR S = 44657VA
By my calcs, I cannot figure out how this is possible. The real power (W) is accurate if you account for losses, but the apparent power (S) proportions are way off. I'm stuck believing it's a function of the drive but is there an explanation or a next step to take to conform this?